Slow Device and Sensor

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Slow Device and Sensor
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:06 AM . Last Modified: ‎2024-04-05 03:37 AM

0 Likes
10
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:06 AM . Last Modified: ‎2024-04-05 03:37 AM

Slow Device and Sensor

Hi,

  We are running DCE 7.4.3 and when new devices are added it can take up to 48 hrs for all the devices sensors to appear. 

Here is an example of a device recently added :

This is the same type device as it should appear 

(CID:126884957)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

0 Likes
4
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

Hi Mark

How many devices are you polling?  At what intervals? 

How much data are you keeping?  What's your trim setting?

Is DCE a VM or a physical server?  If VM, what is the disk performance in IOPS?

When was DCE last restarted?

Cheers

Ed

(CID:126884966)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

In response to DCIM_Support
0 Likes
0
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

Just to add to Ed's questions/comments,

Also look at the repository settings. Is it getting full? Have you tried purging?

If it is a VM as Ed asked, have you given it an extra hard drive?

Does this happen to any new device or just this one?

(CID:126885246)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

In response to DCIM_Support
0 Likes
0
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

Hi Guy's,

  Polling 2662 devices, polling details below. Device is a physical server and was last restarted approx 3 months ago. 

 

(CID:126886024)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

In response to DCIM_Support
0 Likes
0
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

Great info Mark

As you have that many devices, I infer it's a DCE Enterprise 2U appliance AP9475.  This is a well provisioned server for most instances.  Please confirm you've left the default polling at 5 minutes. 

 

The only thing I can recommend is that you push polling out for selected devices. Many DCE users increase the polling interval for devices that don't need such "aggressive" polling.  E.g. they change polling of rack PDUs / power rails from default to say 15 minutes or even an hour.  Little if anything is lost and since rPDUs are often by far the most populous device type, a great benefit can be achieved for little down side by decreasing the polling CPU and IO load on the server. But of course each site is different and only you can make such an assessment.  I believe you can easily change the polling interval for multiple devices in a single command but sadly cant recall how to do that.  This is just a guess at whats happening and without being at your DCE system I cant make a more informed recommendation.

Even if you decide that this is not a solution (or work around) for you, trying this and noting the result will help in deciding next steps.

Kind regards

Ed

 

(CID:126886028)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

In response to DCIM_Support
0 Likes
0
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:37 AM

Hi Mark,

 

I noticed that the most data is in the “other” category. That’s usually an indication that the information is coming in faster than the server can process it. Ed’s suggestion about slowing the polling frequency is absolutely the best place to start. SNMP devices alone however don’t usually have such an issue with memory.

Do you also use NetBotz with cameras?  If so, I’d also look into lowering frame rate and resolution. 

For both SNMP and NetBotz, if the devices are alerting too often, resolving said issues will also lower throughput to the server allowing it to better keep up with the incoming data. 

Steve. 

(CID:126886030)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

0 Likes
2
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

Dear Mark Tucker,

From your screenshots you can clearly see that this equipment Enlogic Co. And the above problem is related only to the hardware of this vendor. Did I get it right?

If so, first you need to make sure, that your DCE-server does not contain more, than one DDF-file for Enlogic hardware. Can you tell which version of the Enlogic DDF-file is on your DCE-server?

In my work I already encountered the problem described by you and for its successful solution it is necessary to have the latest version of DDF-file Enlogic, and it should be only in one copy on the DCE-server (old versions of DDF-files must be deleted).

I think it will be very interesting for you to read Anonymous User comment in topic  on Enlogic equipment. Anonymous User himself faced and solved a similar problem with Enlogic equipment. At the same time, the current version of the DDF-file for Enlogic equipment is v23.

I hope this helps you.

If you have any questions, please ask.

(CID:126885787)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

In response to DCIM_Support
0 Likes
0
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

Hi,

   Thanks for the response, unfortunatly the issue is effecting more than juts the enlogic devices.

 

 

(CID:126885847)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

In response to DCIM_Support
0 Likes
0
963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

Ok, then you better accurately publish with which devices which vendors you are experiencing the above mentioned problems (for example, native APC/Schneider Electric devices or 3-rd party devices)?

And of course, if this is a 3-rd party devices, what versions of the DDF-files do you use in the DCE-server?

With respect.

(CID:126885852)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:07 AM . Last Modified: ‎2024-04-05 03:36 AM

Dear Mark Tucker,

Have you been able to solve your issue or not?

With respect.

(CID:128062200)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:08 AM . Last Modified: ‎2023-10-22 03:56 AM

0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:08 AM . Last Modified: ‎2023-10-22 03:56 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of