Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Simple PUE to be shown in DCE as sensor from DCO

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Simple PUE to be shown in DCE as sensor from DCO
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
78
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:37 PM

0 Likes
25
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:37 PM

Simple PUE to be shown in DCE as sensor from DCO

This question was originally posted on DCIM Support by Boris Majdandzic on 2018-10-10


Is there option or a patch to add Simple PUE from DCO to DCE as a sensor?

Can this be added?

This could be usefull, as you could have value in monitoring at DCE & it would simplify systhem check to a user.

(CID:134681809)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 25
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:37 PM

0 Likes
13
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:37 PM

This answer was originally posted on DCIM Support by Ed Tarento on 2018-10-11


Hi Boris

I haven't done it explicitly with the DCO SNMP agent specifically but there is (or used to be) a feature in the SNMP agent that enables scripted custom OIDs.  I've done this before successfully (but many years ago).  We would need to check that the simple PUE calc built into DCO (not EE) was available programatically (e.g. API, or Export DB call) and then craft this into a custom OID on the SNMP agent.  I think that might meet your exact requirement as stated

But perhaps your business requirement is broader?  You might also explore embedding the DCO PUE widget into a web page/ StruxureWare Portal or similar.  And other may suggest other solutions.  Let me know if you like more info

Cheers

Ed

 

(CID:134682087)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:37 PM

In response to DCIM_Support
0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:37 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-11


Hi, if there is option to use OID it would be great. On portal you cant place "simple" PUE(now on just PUE) from DCO, because it is restricted. I asked Jeff Faridi on this subject personaly. 

Since DCO is monitored by DCE in this case, I would like to use PUE, because this is one of my clients wishes, so he doesn`t have to open DCO web gui.

(CID:134682258)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:37 PM

In response to DCIM_Support
0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:37 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-23


Hi,

Is there a possibilit to get OID, because you can`t put PUE on Portal page. It is restricted.

Do you have another way to read PUE value DCE?

(CID:134687984)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:37 PM

In response to DCIM_Support
0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:37 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-10-23


Hi Boris

I have confirmed I can get the DCO simple PUE value programmatically and if the SNMP agent behaves as I expect then I believe I can craft this feature.    This will require several hours of effort and is in my to do queue.  I can't put this type of work at the top of my list right now but will post my progress as I make it.

Cheers

Ed 

(CID:134688233)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:37 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:37 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-24


Hi Ed,

Thank you , this would be great, because it is the value customer would like to have.

(CID:134688507)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-10


Boris

I've done the necessary tinkering.

Good news is that I can get the DCO PUE figure (not EE) to appear in the DCE.

Bad news is that the transport mechanism used between DCE and DCO (SNMP) does not carry real numbers, only integers.  If anyone has a contrary point of view, please let me know.

That means you can get:

A) a PUE with the decimal places dropped, i.e. 1.9 becomes 1 as does 1.01 or;

B) a PUE multiplied by say 100, so 1.7 shows as 170, 2.35 shows as 235.

I hope that makes sense.  I also hope someone can show me how to carry real numbers (e.g. 1.65) via SNMP.

Let me know if you're interested in progressing and which poison is your preference.

Cheers

Ed

(CID:134695818)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-11


Thinking more about it, this challenge might be addressed with the DCE DDF.  So I'll craft option B) and see what we can do from there.

 

(CID:134696059)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-12


Here's option B)

(CID:134696156)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by spezialist on 2018-11-12


Dear Ed Tarento,

I am interested in this topic: it is easier for me to create a separate DDF-file for DCO (PUE). Since you have already noticed, that standard DCE software Supplemental OIDs do not allow the decimal point to be processed.

With respect.

(CID:134696178)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-12


Hello Ed & spezialist,

Sorry for silence, but last week I was on site building new data center & only had on-line abilities in the evening.

If there is possibility to get the separate ddf file it would be great.

For now I think that Ed`s option B is more acceptable.

I will use it to show it to client & think he will be very happy.

(CID:134696202)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-12


Hi Ed Tarento, 

Can you please help me setup option B.

the OID is the one u send in picture I presume?

(CID:134696231)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-12


 

With a prompt by Greg Sterling I think I may have worked a way to get the exact PUE to DCE (so no need to fiddle with DDF, thanks anyway spezialist).  I'm waiting til tomorrow when DCO PUE updates with a new value to see how that works in the DCE graph.  I'll then write up some instructions for you.  The solution currently looks like:

and

Cheers

Ed

(CID:134696512)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:38 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:38 PM

This comment was originally posted on DCIM Support by spezialist on 2018-11-13


Ok, thanks for the helpful info.

With respect.

(CID:135431860)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-13


Hi Ed,

That is excellent news. If possible send me instructions so I can import it in my presentation in 2 days.

Thanks for your help. If you need anything I am able to help with, just ask.

(CID:135432167)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

0 Likes
7
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This answer was originally posted on DCIM Support by Ed Tarento on 2018-11-14


DCO PUE is available in DCE.  See instructions DCO PUE in DCE.pdf

(CID:135433083)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This comment was originally posted on DCIM Support by spezialist on 2018-11-15


Dear Ed Tarento,

Unfortunately:

DCO PUE is available in DCE.  See instructions [attachment deducted]

With respect.

(CID:135433239)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-15


Hi,

Since you want to remove tha att, I presume this isn`t something users should do, or do I have to ask this through feature request?

(CID:135433486)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-19


Hi spezialist and Boris Majdandzic

I don't understand your posts, Nov 15 & 16.  AFAIK, there is no problem making these modifications but they are unsupported, by SE or myself.  I can try to help but there is no guarantee of success or future interoperability.  We just do our best to help the community.  I hope this helps.

Cheers

Ed

(CID:136153052)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This comment was originally posted on DCIM Support by spezialist on 2018-11-19


Dear Ed Tarento,

I would like to draw your attention to this:

You incorrectly attached the file. And now it is not available to anyone.

With respect.

(CID:136153059)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-19


Hello,

I am still able to see the attachment & download it.

I thougt it will break the contract if I do this myself, so it will be removed.

(CID:136153129)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:39 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:39 PM

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-19


Boris, if you are concerned about your contract and wish to confirm, I recommend you check with SE about applying this modification

Kind regards

Ed

(CID:136153382)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:40 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:40 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-20


Thanks Ed.

(CID:136153897)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:40 PM

0 Likes
1
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:40 PM

This answer was originally posted on DCIM Support by Ed Tarento on 2018-11-19


I've posted a new tip .  Can you see it now?

(CID:136153392)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:40 PM

In response to DCIM_Support
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:40 PM

This comment was originally posted on DCIM Support by spezialist on 2018-11-19


Dear Ed Tarento,

Yes, of course, now I see the download link:


Thanks for the great job 😀.

(CID:136153398)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 12:40 PM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-05 12:40 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc