Simple PUE to be shown in DCE as sensor from DCO

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
25
825

Simple PUE to be shown in DCE as sensor from DCO

This question was originally posted on DCIM Support by Boris Majdandzic on 2018-10-10


Is there option or a patch to add Simple PUE from DCO to DCE as a sensor?

Can this be added?

This could be usefull, as you could have value in monitoring at DCE & it would simplify systhem check to a user.

(CID:134681809)

25 Replies 25
DCIM_Support
Picard
Picard
0 Likes
13
825

Re: Simple PUE to be shown in DCE as sensor from DCO

This answer was originally posted on DCIM Support by Ed Tarento on 2018-10-11


Hi Boris

I haven't done it explicitly with the DCO SNMP agent specifically but there is (or used to be) a feature in the SNMP agent that enables scripted custom OIDs.  I've done this before successfully (but many years ago).  We would need to check that the simple PUE calc built into DCO (not EE) was available programatically (e.g. API, or Export DB call) and then craft this into a custom OID on the SNMP agent.  I think that might meet your exact requirement as stated

But perhaps your business requirement is broader?  You might also explore embedding the DCO PUE widget into a web page/ StruxureWare Portal or similar.  And other may suggest other solutions.  Let me know if you like more info

Cheers

Ed

 

(CID:134682087)

DCIM_Support
Picard
Picard
0 Likes
0
825

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-11


Hi, if there is option to use OID it would be great. On portal you cant place "simple" PUE(now on just PUE) from DCO, because it is restricted. I asked Jeff Faridi on this subject personaly. 

Since DCO is monitored by DCE in this case, I would like to use PUE, because this is one of my clients wishes, so he doesn`t have to open DCO web gui.

(CID:134682258)

DCIM_Support
Picard
Picard
0 Likes
0
825

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-23


Hi,

Is there a possibilit to get OID, because you can`t put PUE on Portal page. It is restricted.

Do you have another way to read PUE value DCE?

(CID:134687984)

DCIM_Support
Picard
Picard
0 Likes
0
825

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Ed Tarento on 2018-10-23


Hi Boris

I have confirmed I can get the DCO simple PUE value programmatically and if the SNMP agent behaves as I expect then I believe I can craft this feature.    This will require several hours of effort and is in my to do queue.  I can't put this type of work at the top of my list right now but will post my progress as I make it.

Cheers

Ed 

(CID:134688233)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-10-24


Hi Ed,

Thank you , this would be great, because it is the value customer would like to have.

(CID:134688507)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-10


Boris

I've done the necessary tinkering.

Good news is that I can get the DCO PUE figure (not EE) to appear in the DCE.

Bad news is that the transport mechanism used between DCE and DCO (SNMP) does not carry real numbers, only integers.  If anyone has a contrary point of view, please let me know.

That means you can get:

A) a PUE with the decimal places dropped, i.e. 1.9 becomes 1 as does 1.01 or;

B) a PUE multiplied by say 100, so 1.7 shows as 170, 2.35 shows as 235.

I hope that makes sense.  I also hope someone can show me how to carry real numbers (e.g. 1.65) via SNMP.

Let me know if you're interested in progressing and which poison is your preference.

Cheers

Ed

(CID:134695818)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-11


Thinking more about it, this challenge might be addressed with the DCE DDF.  So I'll craft option B) and see what we can do from there.

 

(CID:134696059)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-12


Here's option B)

(CID:134696156)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by spezialist on 2018-11-12


Dear Ed Tarento,

I am interested in this topic: it is easier for me to create a separate DDF-file for DCO (PUE). Since you have already noticed, that standard DCE software Supplemental OIDs do not allow the decimal point to be processed.

With respect.

(CID:134696178)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-12


Hello Ed & spezialist,

Sorry for silence, but last week I was on site building new data center & only had on-line abilities in the evening.

If there is possibility to get the separate ddf file it would be great.

For now I think that Ed`s option B is more acceptable.

I will use it to show it to client & think he will be very happy.

(CID:134696202)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-12


Hi Ed Tarento, 

Can you please help me setup option B.

the OID is the one u send in picture I presume?

(CID:134696231)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-12


 

With a prompt by Greg Sterling I think I may have worked a way to get the exact PUE to DCE (so no need to fiddle with DDF, thanks anyway spezialist).  I'm waiting til tomorrow when DCO PUE updates with a new value to see how that works in the DCE graph.  I'll then write up some instructions for you.  The solution currently looks like:

and

Cheers

Ed

(CID:134696512)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by spezialist on 2018-11-13


Ok, thanks for the helpful info.

With respect.

(CID:135431860)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-13


Hi Ed,

That is excellent news. If possible send me instructions so I can import it in my presentation in 2 days.

Thanks for your help. If you need anything I am able to help with, just ask.

(CID:135432167)

DCIM_Support
Picard
Picard
0 Likes
7
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This answer was originally posted on DCIM Support by Ed Tarento on 2018-11-14


DCO PUE is available in DCE.  See instructions DCO PUE in DCE.pdf

(CID:135433083)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by spezialist on 2018-11-15


Dear Ed Tarento,

Unfortunately:

DCO PUE is available in DCE.  See instructions [attachment deducted]

With respect.

(CID:135433239)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-15


Hi,

Since you want to remove tha att, I presume this isn`t something users should do, or do I have to ask this through feature request?

(CID:135433486)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-19


Hi spezialist and Boris Majdandzic

I don't understand your posts, Nov 15 & 16.  AFAIK, there is no problem making these modifications but they are unsupported, by SE or myself.  I can try to help but there is no guarantee of success or future interoperability.  We just do our best to help the community.  I hope this helps.

Cheers

Ed

(CID:136153052)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by spezialist on 2018-11-19


Dear Ed Tarento,

I would like to draw your attention to this:

You incorrectly attached the file. And now it is not available to anyone.

With respect.

(CID:136153059)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-19


Hello,

I am still able to see the attachment & download it.

I thougt it will break the contract if I do this myself, so it will be removed.

(CID:136153129)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Ed Tarento on 2018-11-19


Boris, if you are concerned about your contract and wish to confirm, I recommend you check with SE about applying this modification

Kind regards

Ed

(CID:136153382)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-11-20


Thanks Ed.

(CID:136153897)

DCIM_Support
Picard
Picard
0 Likes
1
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This answer was originally posted on DCIM Support by Ed Tarento on 2018-11-19


I've posted a new tip .  Can you see it now?

(CID:136153392)

DCIM_Support
Picard
Picard
0 Likes
0
826

Re: Simple PUE to be shown in DCE as sensor from DCO

This comment was originally posted on DCIM Support by spezialist on 2018-11-19


Dear Ed Tarento,

Yes, of course, now I see the download link:


Thanks for the great job 😀.

(CID:136153398)

DCIM_Support
Picard
Picard
0 Likes
0
826