Siemens 9510 Power Meter Modbus Gateway Issue

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Siemens 9510 Power Meter Modbus Gateway Issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
63
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

0 Likes
8
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

Siemens 9510 Power Meter Modbus Gateway Issue

We have a few circuit breakers that are daisy-chain connected to Siemens 9510 power meter's COM1. We try to monitor the power meter and the circuit breaker via MODBUS.

Before enabling Modbus gateway on the 9510 meter, I was able to retrieve all power meter sensors from DCE with slave id 1.

After enabling Modbus gateway (COM1 protocol set as EtherGate or Modbus Master). I was not able to retrieve any power meter sensors. DCE only showed the Link Status. The link was also not stable. It went up and down.

I called ION support. They think it might be DCE issue. They used MODBUS tester tool and confirmed the tool can retrieve PM data with slave id 255.

Can you please help?

(CID:105474304)

Labels
  • Labels:
  • Data Center Expert
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

0 Likes
6
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

I have a similar problem, an d i put slave id 255 and go fine

(CID:105474313)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

DCE only allows slave id ranging from 1 to 247 though.

(CID:105474315)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:21 AM . Last Modified: ‎2024-04-09 12:19 AM

Upgrade DCE 7.3.1

(CID:105474321)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:19 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:19 AM

We are using 7.2.7. I will upgrade our DCE to 7.3.1. By the way, how do you determine the slave ids of the circuit breakers that are connected to the power meter?

(CID:105474329)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:18 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:18 AM

In my case, it see like a gateway all the elements

(CID:105474330)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:18 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:18 AM

Do you configure power meter COM1 as EtherGate or Modbus Master? When I configure it as EtherGate, I could communicate with power meter using 255. I could not communicate with slaves with slave addresses. When I configured it as MODBUS Master, I could communicate with power meter using 255 and slaves with their addresses.

(CID:106205228)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:18 AM

In response to DCIM_Support
0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2024-04-09 12:18 AM

In my case i use as ethergate but it's on PM off Schneider, but can you use as master if you need to communicate PM and slaves

(CID:106207121)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2023-10-31 11:35 PM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:22 AM . Last Modified: ‎2023-10-31 11:35 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of