We are unable to access "Server Configuration"/Webmin on an upgraded DCO 7.4.5 server using the latest version of Chrome and Firefox.
In Firefox 35.0.1 you get:
Unable to Connect Securely
Firefox cannot guarantee the safety of your data on
Advanced info: ssl_error_no_cypher_overlap
In Chrome 40.0.2214.111 (64-bit) you get:
This webpage is not available
A secure connection cannot be established because this site uses an unsupported protocol.
Error code: ERR_SSL_VERSION_OR_CIPHER_MISMATCH
(CID:94602069)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-02 11:01 AM . Last Modified: ‎2024-04-10 12:41 AM
When using an DCO server upgraded to version 7.4.5 and trying to access the "Server Configuration"/Webmin interface an error is shown when using latest Firefox or Chrome browser.
A manuel workaround is to go into "Server Configuration" / Webmin https://
"Webmin" -> "Webmin Configuration" -> "SSL Encryption" -> Set "SSL protocol version" to "10"
(CID:110017372)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-02 11:02 AM . Last Modified: ‎2023-10-31 11:36 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.