SNMPV3 - Value Not Supported

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • SNMPV3 - Value Not Supported
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

0 Likes
3
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

SNMPV3 - Value Not Supported

Dear Support,

We are converting devices which are already discovered type SNMPV1 in DCE to SNMPV3. After conversion, the devices are online on DCE using SNMPV3 and everything is normal. BUT, during the conversion, DCE gave a message "Value Not Supported" on all the devices and the SNMP configuration on APC devices showed Transfer Incomplete. 

Note that the authentication password used is in the form; xxxxxxxxxx@123456 (total 17 characters) and the message is as shown in the picture below;

Kindly advise what is the meaning of "Value Not Supported" and if there is any action to be taken, keeping in mind that all devices are discovered and online on DCE. 

Thank you in advance,

Best Regards,

(CID:141271065)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

0 Likes
1
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

Hi Hrant,

To change the SNMP version after devices have already been discovered, I strongly recommend following k-base FA158442. That document also states the following:

NOTE: The the configuration status will show as Incomplete Configuration, as DCE is unable to verify the changes due to security reasons.  You can view additional details by right-clicking and then selecting Show Configuration Results.

Basically there are some settings such as passwords that are not able to be retrieved from the device using FTP for security reasons so when DCE tries to check the sent information with the retrieved information after the update, it may error out. 

 

You mentioned "Value Not Supported". Can you show, in a screenshot maybe, exactly where / when you're receiving this error? You mentioned a picture but I do not see it attached. It's not the incomplete configuration I just mentioned, is it?

Is that error specific to that passcode: xxxxxxxxxx@123456 (total 17 characters)? Have you tried different characters? I tried a similar paradigm when creating a template and do not see this error entering the values:

User name and both phrases were the same - abcdefghij@123456

I added them manually to an NMC running 6.5.0 firmware and had no issues. I then used DCE to configure an NMC. Again, all I received was the expected error noted in the above k-base:

 

Thanks,

Steve

 

 

(CID:141271290)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

0 Likes
1
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

Hi Hrant,

To change the SNMP version after devices have already been discovered, I strongly recommend following k-base FA158442. That document also states the following:

NOTE: The the configuration status will show as Incomplete Configuration, as DCE is unable to verify the changes due to security reasons.  You can view additional details by right-clicking and then selecting Show Configuration Results.

Basically there are some settings such as passwords that are not able to be retrieved from the device using FTP for security reasons so when DCE tries to check the sent information with the retrieved information after the update, it may error out. 

 

You mentioned "Value Not Supported". Can you show, in a screenshot maybe, exactly where / when you're receiving this error? You mentioned a picture but I do not see it attached. It's not the incomplete configuration I just mentioned, is it?

Is that error specific to that passcode: xxxxxxxxxx@123456 (total 17 characters)? Have you tried different characters? I tried a similar paradigm when creating a template and do not see this error entering the values:

User name and both phrases were the same - abcdefghij@123456

I added them manually to an NMC running 6.5.0 firmware and had no issues. I then used DCE to configure an NMC. Again, all I received was the expected error noted in the above k-base:

 

Thanks,

Steve

 

 

(CID:141271290)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

In response to DCIM_Support
0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2024-04-03 02:53 AM

Hello Steven,

Thank you very much for your quick response,

I have checked the document you recommended and watched the video and what happened with us is the same as in the video. 

I verified it as per the video steps and all devices now are on SNMPV3. 

Thanks again for your support,

Have a nice day!

Hrant

(CID:141271515)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2023-10-22 03:49 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:43 PM . Last Modified: ‎2023-10-22 03:49 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of