Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

SNMP data type opaque

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • SNMP data type opaque
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Gabi
Lieutenant Gabi
Lieutenant

Posted: ‎2023-03-10 08:43 AM

0 Likes
6
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-10 08:43 AM

SNMP data type opaque

Hi,

 

there is a plan to implement on DCE, option to handle data type opaque?

 

thanks

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Shaun
Commander Shaun Commander
Commander

Posted: ‎2023-03-10 10:47 AM

0 Likes
0
2246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-10 10:47 AM

Hi Gabi,

 

Could you help me understand, what kind of data you envisage capturing this way, and what value that data brings?

 

DCE is typically interested in data which is either scalar or stateful - things we can measure, graph, compare and act on.  Opaque types are usually difficult for this because if the data means nothing to the DCE, then all we're doing is warehousing it - which does not play to the DCE's strengths at all.

 

It is something that could be looked at, but we'd need to better understand the payoff, or "user story".

Reply

Link copied. Please paste this link to share this article on your social media post.

Gabi
Lieutenant Gabi
Lieutenant

Posted: ‎2023-03-10 08:16 PM

0 Likes
1
2240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-10 08:16 PM

Hi Shaun,

 

like usual Vertiv reinvent the wheel in the monitoring system and the new CRAC/CRAH units comes equipped with different Carel controllers and monitoring modules

 

this new monitoring modules use data type opaque and from interface I can change to integer/unsigned but response contains only 2 digit like temperature 21.5 with opaque remains 21 on integer/unsigned(I`m not sure but even worse the value is rounded up ) 

 

DCE ignore all oid configured in DDF that are set as opaque on Vertiv monitoring module

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2023-03-12 11:39 AM

In response to Gabi
0 Likes
0
2230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-12 11:39 AM

HI Gabi,

 

Thanks, that makes a lot more sense.  I can see what they're trying to do - the only native snmp type for decimal values is using floats, which are an expensive operation for many embedded controllers.  (This is why a lot of APC oids use "tenths of an amp" & similar, to provide decimal precision without having to send decimal values).

 

Would it be possible to do an snmp walk from the DCE's web interface (the Status link top-right, and pick snmp walk from the menu) and share how this particular oid appears there?  (No need to share the whole thing, just the entry for this specific example will do me).

 

Thanks,

  Shaun

Reply

Link copied. Please paste this link to share this article on your social media post.

Gabi
Lieutenant Gabi
Lieutenant

Posted: ‎2023-03-12 08:53 PM

0 Likes
0
2225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-12 08:53 PM

Hi Shaun,

 

 

for example return temperature which is ending with .540.0 on previous screenshot is shown in different ways by mib browser, DCE snmp walk and Schneider windows walk app for DDF support

 

windows walker Schneider(seem like doesn`t know to decode the value)

1.3.6.1.4.1.476.1.42.4.3.32.540.0, Opaque      , ďż˝xAďż˝ff

 

mib browser

Name/OID: .1.3.6.1.4.1.476.1.42.4.3.32.540.0; Value (Opaque): 22.3

 

web walker DCE

.1.3.6.1.4.1.476.1.42.4.3.32.540.0 = Opaque: Float: 22.299999

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Gabi
Lieutenant Gabi
Lieutenant

Posted: ‎2023-03-20 03:19 AM

0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-20 03:19 AM

Hi @Shaun,

 

do you have any answer regarding this problem?

 

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2023-03-21 01:40 PM

0 Likes
0
2156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 01:40 PM

Hi @Gabi,

 

I was off ill last week, sorry for the delay.

 

My plan going forward is to replicate this and see what our options are.  If it's possible to manipulate in the DDF I'll share what I find (on a "best effort" basis - we don't support customers creating their own DDFs, so what you do with those findings will be your problem).  But if it requires a feature/enhancement request in the DCE, there'll be very little I can share from there.  There's a line between being helpful, and "how the sausage is made", that I need to tread carefully.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of