Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-13 09:03 AM . Last Modified: 2023-02-13 09:05 AM
Hello everyone,
Im working with Servertech PDU's and I would like to add them to my Struxtureware monitoring version 7.2.0.512.
Im trying to have them discovered by adding them as a SNMPv1 but seems like they are unable to be discovered.
Anyone can help on this please? My Servertech PDU's dont have the latest software so they do not have the ability to pull out the power consumption logs from their network card directly. I want to be able to monitor my consumption on struxureware
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-13 11:51 PM . Last Modified: 2025-08-12 05:16 AM
Hi Mel,
You might want to post your PME (Power Monitoring Expert) related issues here:
https://community.se.com/t5/EcoStruxure-Power-Monitoring/bd-p/power-monitoring-expert
you may need to login or register.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-17 06:09 AM
Hi,
I assume you are mentioning DCE 7.2.0.
1. You may need to add the DDF for ServerTech PDU from https://ddf.ecostruxureit.com/ and look for ServerTech PDU. Download the DDF and add into DCE, and rediscover the device again.
2. I suggest you update the DCE to the latest version (7.2.0 is a bit old). You can reach out the local sales to engage for software support contact for DCE and entitle to DCE upgrade.
BR,
TJ
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-14 09:40 AM
Hello TJ,
Thank you! I was able to download my DDF file!! I still have an issue... Just noticed that my PDU's are not protected and therefore, are not login in throught HTTPS but rather just HTTP... and are using users and passwords...
this seems to block the discovery of my PDU's. Can it? If so, is there a way to bypass this so they can be discovered anyways?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-24 01:33 AM . Last Modified: 2025-05-26 12:07 AM
Hi,
Sorry for the late update. To discover 3rd party SNMP devices, you may refer to the kb as follows:
https://www.se.com/us/en/faqs/FA383264/
BR,
TJ
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.