Posted: 2020-07-04 06:18 PM
This question was originally posted on DCIM Support by Aleksey Kilin on 2018-05-30
Hello
After upgrade DCE to version 7.5 all sensors of power bank in rpdu is unplugged
See picture :
But before upgrade it was ok also see picture :
I also download a new ddf file version 49 but still unplugged.
Please what can you advise?
Thank you
(CID:131967144)
Posted: 2020-07-04 06:18 PM
This answer was originally posted on DCIM Support by spezialist on 2018-05-30
Dear Aleksey Kilin,
This is a known bug in the DDF-file, which I already reported (for example, see my post After upgrade to DCE-7.5.0: chained rPDUs "Power Bank" sensors switched to Unplugged) and which should have been fixed...
In order to check if this bug is fixed in the new version v.49 DDF-file, you need to remove all Unplugged sensors and make Request Device Scan again. Be sure, do not forget before that, make a full backup of your DCE-server. If after this, the above-mentioned power bank sensors do not appear, then unfortunately, the bug have not been fixed ☹️.
Please try and report the result.
With respect.
(CID:131967183)
Posted: 2020-07-04 06:18 PM
This answer was originally posted on DCIM Support by Balaraman Jagadeesan on 2018-05-30
Dear Aleksey,
I have found the following K-base document which addresses your query.
https://www.schneider-electric.co.in/en/faqs/FA282386/
K-base title: Why does StruxureWare DCE show duplicate sensors after upgrade, one of the duplicates reports unplugged.
I hope this helps.
Regards,
Bala
(CID:131967169)
Posted: 2020-07-04 06:18 PM
This answer was originally posted on DCIM Support by spezialist on 2018-05-30
Dear Aleksey Kilin,
This is a known bug in the DDF-file, which I already reported (for example, see my post After upgrade to DCE-7.5.0: chained rPDUs "Power Bank" sensors switched to Unplugged) and which should have been fixed...
In order to check if this bug is fixed in the new version v.49 DDF-file, you need to remove all Unplugged sensors and make Request Device Scan again. Be sure, do not forget before that, make a full backup of your DCE-server. If after this, the above-mentioned power bank sensors do not appear, then unfortunately, the bug have not been fixed ☹️.
Please try and report the result.
With respect.
(CID:131967183)
Posted: 2020-07-04 06:19 PM
This comment was originally posted on DCIM Support by Aleksey Kilin on 2018-05-30
Thank you for your answer
Recently i add new pdu's after that i install new ddf but sensors do not appear then i think bug still exist .
See picture:
(CID:131967194)
Posted: 2020-07-04 06:19 PM
This comment was originally posted on DCIM Support by spezialist on 2018-05-30
Dear Aleksey Kilin,
We conclude, that the bug has not been fixed even in the latest version of the DDF-file v.49 ☹️.
Ok, I will privately share with you my email address. Can you send me your new v.49 DDF-file? I can analyze it and say exactly about the presence of the bug.
With respect.
(CID:131967210)
Posted: 2020-07-04 06:19 PM
This comment was originally posted on DCIM Support by Aleksey Kilin on 2018-05-31
Hi
Can you share you email then i will send you ddf file.
Thank you
(CID:132646629)
Posted: 2020-07-04 06:19 PM
This comment was originally posted on DCIM Support by spezialist on 2018-05-31
Ok, I resend my email address (see your mailbox).
(CID:132646632)
Posted: 2020-07-04 06:19 PM
This comment was originally posted on DCIM Support by Aleksey Kilin on 2018-05-31
I didn't receive
(CID:132646647)
Posted: 2020-07-04 06:19 PM
This comment was originally posted on DCIM Support by spezialist on 2018-05-31
It is strange, why on your personal mail box does not come the message with my e-mail...
(CID:132646657)
Posted: 2020-07-04 06:19 PM
This comment was originally posted on DCIM Support by spezialist on 2018-05-31
Dear Aleksey Kilin,
I'm sending you an v.49 apcpower.xml DDF-file with a fixed bugs for the bank's power sensors. For me, this DDF-file works fine.
Try and tell me please the result.
With respect.
(CID:132646729)