EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 07:01 AM . Last Modified: β2024-04-08 04:19 AM
Hi fellows,
BR,
SameehMISSING IMAGE: Cooling map error megssage tha I receive_Aisle1 _after mod.png
(CID:108828611)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 07:01 AM . Last Modified: β2024-04-08 04:19 AM
Hi Sameeh,
It seems you've tried to fill the gaps with "blocks" in the containment systems. I don't think that we properly support this.
And for modeling the hot aisle and/or cold aisle containment systems, racks and other units should be inside the containment systems. But please notice that:
when modeling a Cold Aisle Containment System, racks (in "rowA") and racks (in "rowB") must be placed front-to-front (eg. creating a cold aisle inside the containment system)
but when modeling a Hot Aisle Containment system, racks (in "rowA") and racks (in "rowB") must be placed back-to-back (hot aisle inside the containment system).
Kind regards
(CID:108828876)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 07:01 AM . Last Modified: β2024-04-08 04:19 AM
Hi Sameeh ahmad, thanks for posting. Lets see who can be of assistance here. @community any ideas? Kind regards Ditte
(CID:108828667)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 07:01 AM . Last Modified: β2024-04-08 04:19 AM
Hi Sameeh,
It seems you've tried to fill the gaps with "blocks" in the containment systems. I don't think that we properly support this.
And for modeling the hot aisle and/or cold aisle containment systems, racks and other units should be inside the containment systems. But please notice that:
when modeling a Cold Aisle Containment System, racks (in "rowA") and racks (in "rowB") must be placed front-to-front (eg. creating a cold aisle inside the containment system)
but when modeling a Hot Aisle Containment system, racks (in "rowA") and racks (in "rowB") must be placed back-to-back (hot aisle inside the containment system).
Kind regards
(CID:108828876)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 07:01 AM . Last Modified: β2024-04-08 04:19 AM
Hi Jef, Thanks for clear description, I have already replcaed the Blocks with Empty Racks and it works well now, but In real site I have concrete blocks in these areas, Is there another way to simulte this concrete ? BR, Sameeh
(CID:108828909)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 07:01 AM . Last Modified: β2023-10-22 03:43 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.