Rack PDU does not give kw value on DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Rack PDU does not give kw value on DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

0 Likes
9
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

Rack PDU does not give kw value on DCE

Hi Community,

 

I can not see rack mount PDU(AP8853&AP8886) kw value on DCE, but it seens rPDU web interface. When i try to create new virtual sensor, it is not working. Each power value is watt. My customer wants to see kw value on DCE. Please can you share me any advance.. You can see attached images.

 

Regards

Kerem

 

RPDU DCE Int..JPG

RPDU Web Int..JPG

 

(CID:105468440)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • Portal
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2024-04-09 12:44 AM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2024-04-09 12:44 AM

Hi guys,

 

Some values are indeed provided by the device and for watts or KW on PDUs some are actually calculated by the DDF as Valentin noted. There may be issues with requesting an updated DDF for APC PDUs. If you get an updated PDU DDF and then the system itself is updated, most server updates also include updated DDF files which will overwrite the one you've put on the system.

 

Additionally, we are discussing the fact that the DDF is responsible for these values. It is believed that the PDU should be responsible for providing these values so if this is changed in the future, you may have to again deal with a value in watts rather than KW. I will forward this on to engineering so they will have more data for this investigation. 

 

Steve.

(CID:105468504)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

0 Likes
6
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

Hi Kerem!

DCE shows values that contains in DDF for corresponding device.

So you need to contact multivendorsupport@apc.com team and request an update for DDF file you use.

 

(CID:105468464)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

In response to DCIM_Support
0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

Thank you for answer Valentin. But one more, i used SNMPv1 discovery type.. So what kind of DDF that i need? and when DDF arrived to me, should i discover again? Regards Kerem

(CID:105468469)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

In response to DCIM_Support
0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

You need a DDF for SNMP protocol. When you receive DFF, you need to upload it to DCE and then sensor values will be updated automatically.

(CID:105468473)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

In response to DCIM_Support
0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

Thank you again Valentin.

(CID:105468493)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

In response to DCIM_Support
0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

Hi Valentin, SNMP Device Defnition file is updated but, still kw value is not available. Do i extra configuration? You can see new ddf file and sensors view in attach. Regards Kerem

apcpower.zip

rack PDU sensors.JPG

(CID:105468814)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

In response to DCIM_Support
0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:03 AM . Last Modified: ‎2024-04-09 12:44 AM

Hi Kerem! Its better if you ask multivendorsupport about that. You need no extra configurations. You can try to discover devices again, but I'm not sure if it helps.

(CID:105469016)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2024-04-09 12:44 AM

In response to DCIM_Support
0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2024-04-09 12:44 AM

[Multivendorsupport] The sensors for Power are present in the DDF for APC Rack PDUs, though measured in Watts, rather than Kilowatts. This is in order to map correctly to sensors in DCO. For this reason, we are unable to change the sensor type to kW as it would break this compatibility.

(CID:105470538)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2024-04-09 12:44 AM

0 Likes
0
1107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2024-04-09 12:44 AM

Hi guys,

 

Some values are indeed provided by the device and for watts or KW on PDUs some are actually calculated by the DDF as Valentin noted. There may be issues with requesting an updated DDF for APC PDUs. If you get an updated PDU DDF and then the system itself is updated, most server updates also include updated DDF files which will overwrite the one you've put on the system.

 

Additionally, we are discussing the fact that the DDF is responsible for these values. It is believed that the PDU should be responsible for providing these values so if this is changed in the future, you may have to again deal with a value in watts rather than KW. I will forward this on to engineering so they will have more data for this investigation. 

 

Steve.

(CID:105468504)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2023-10-31 11:32 PM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:04 AM . Last Modified: ‎2023-10-31 11:32 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of