RFID not communicating with DCO

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • RFID not communicating with DCO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:19 AM

0 Likes
7
978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:19 AM

RFID not communicating with DCO

We have installed the DCO 8.3 .2 version and created the Server rooms and devices ,
Here we have RFID devices (Manufacturer : RFCode , Software : Centerscape )connected in Each Server for monitoring ,
While trying to integrate DCO with RFID we are facing some problem in ETL configuration part

In DCO not able to find the RFcode in the external system configuration part

please guide how to configure RFCode in DCO

(CID:149786649)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:19 AM

0 Likes
5
977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:19 AM

Hello Pradeeep

A general overview of setting up the connector can be found here: https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/RF+Code+CenterScape+Connector

I will note the method of adding an etl configuration has changed since the above link was created. ETL maintenance is now completed in the DCO web client, not webmin.

So from the DCO web client logon as an administrator user. From the below settings icon click "manage ETL configuration"

fill-in the popup page. Make sure you define an IMPORT database, set the name and user credentials for connecting to the database and its critical you define an allowed list otherwise a connection to the database will not be allowed.

Notice in my above example I used a network mask format "0.0.0.0/0" which allows connections from anywhere, in your case you may want to be more restrictive.

Click Next.

From the next page you should see the rfcode connector item in the drop down list

Fill in the proper values for the other fields.

(CID:149786731)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

In response to DCIM_Support
0 Likes
0
977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

The same method has been followed over and over, post configuration the desired output was not received as RFID tags are not been reflected in the DCO server, we saw only one tag and same was shown in the below screenshots.

 

ETL configuration has been done in the last week, please check the screenshots for the same.

                                               ETL for RFID.docx                                          

(CID:151063692)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

In response to DCIM_Support
0 Likes
0
978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

Hello Pradeep.

Your attachment is helpful in that I can see you indeed have what looks like rfcode assets listed in the unassociated items list (per the below screenshot).

Have you associated the above entries from the unassociated items list to assets in DCO? Your custom properties and tags will not appear in DCO until those above items in the list are dragged or associated onto a DCO asset. This means you will not see tag data for any of the items in the above list.

Once that has been completed, re-run the ETL job, tags should then appear on your devices assuming the tag entries exist in the import database.

Regards

Greg Sterling

(CID:151063673)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

In response to DCIM_Support
0 Likes
0
978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

Also, if you review the contents of the configuration_item_property table in the import database, is the tag data you're looking for present in the table?

I pasted a simple example below for a custom property (tags have a different value in the pt_id field).

Are the tag entries you expect to see present in this table, and what is the value in the "state_flag" column? Are they "new", "changed" or "synced"?

(CID:151063688)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

In response to DCIM_Support
0 Likes
0
978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

I also see in an email I received you're having trouble connecting to the staging database as the password has been forgotten.

 

If you logon to the web client and go to the ETL configuration view, if you click the edit button

 

Then edit the password value in the setting windows for the configuration, click submit and the database password will be changed to the specified password. Then use the connection and credential info based on the contents of this page.

 

(CID:151063680)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

In response to DCIM_Support
0 Likes
0
978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2024-04-03 12:18 AM

I received your email. The allowed list in the below screenshot you sent is very specific. In the screenshot you are stating IP 172.17.67.100 can access database staging_centerscape1 using the creds you defined. I assume that IP is the IP of the centerscape server?

DCO Server IP: 172.17.67.99

Client PC IP: 172.17.166.130 

But that IP is not the PC or DCO server IP. Can you add or change that IP to something like a subnet range or add a list of IP's but clicking the "+" button to include the PC and DCO server in the allowed list?

 

 

(CID:151584847)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2023-10-22 03:42 AM

0 Likes
0
978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:54 PM . Last Modified: ‎2023-10-22 03:42 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of