Problems with TRAC2042 (PcoWeb) and DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Problems with TRAC2042 (PcoWeb) and DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

0 Likes
8
1075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

Problems with TRAC2042 (PcoWeb) and DCE

I can not integrate properly my Uniflair TRAC2042 with DCE. Any suggestions?

Thank you

(CID:105469848)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

0 Likes
1
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

Hi Frederico,

 

To get the proper DDF files for your device, you'll want to contact multivendorsupport@apcc.com. They should be able to provide or create the proper one for your device. There is a caveat however when discovering a PCOweb device. The PCOweb is used on many different devices. The OID that is usually used to describe the specific device only describes the PCOweb card and not what it is connected to. SNMP DDFs are associated automatically. The problem there is we can not determine which device or model it is so we can not determine which PCOweb SNMP DDF to use.  If you have multiple different types of devices using the PCOweb card and SNMP, DCE will be unable to distinguish between them and use the first PCOweb DDF it finds if there are multiple installed.


If you use Modbus, you should not have this issue. With the proper DDF installed, you actually choose the DDF when you discover the device so as long as the DDF is for that device and is written properly, there is no way the system will auto-select the wrong DDF for you. I did see one that responder note that he had similar issues with a Modbus DDF so that is likely the issue, either the wrong DDF or the DDF was reading improper registers or formatting them incorrectly.


Steve

(CID:105470052)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

I have a similiar problem with a PCOweb 5 and a Uniflair ISCF0921A and the DDF files, do tou have the TRAC2042's DDF files ?

(CID:105470272)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

0 Likes
1
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

HI Federico!

Can you describe your problem more detail? What problem you faced on?

(CID:105469916)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

In response to DCIM_Support
0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

I have a Uniflair TRAC2042 which is connected by a PcoWeb , and I want to add it to the DCE.

If I make detection by the type SNMPv1, recognizes it as a workstation/server Linux and no device's sensors appears.

 

If I make the search via TCP Modbus and I select device type "Uniflair TRA Chiller (Modbus TCP)", which correspond to the team I have, recognizes it but when I want to see the sensors many are listed as disconnected and others with wrong values.

And a permanent alert "alarm Type A"

(CID:105470264)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:28 AM . Last Modified: ‎2024-04-09 12:35 AM

Do you have DDF files for SNMP or MODBUS?, In my case, that was similar, by SNMPv1 i obtain The same a workstation/server Linux before i put the DDF files, Now with it, have the same problem as you in MOdbus, many sensor have wrong values, but i don´t have sensor as disconnect

(CID:105470274)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

0 Likes
1
1077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

Hi Frederico,

 

To get the proper DDF files for your device, you'll want to contact multivendorsupport@apcc.com. They should be able to provide or create the proper one for your device. There is a caveat however when discovering a PCOweb device. The PCOweb is used on many different devices. The OID that is usually used to describe the specific device only describes the PCOweb card and not what it is connected to. SNMP DDFs are associated automatically. The problem there is we can not determine which device or model it is so we can not determine which PCOweb SNMP DDF to use.  If you have multiple different types of devices using the PCOweb card and SNMP, DCE will be unable to distinguish between them and use the first PCOweb DDF it finds if there are multiple installed.


If you use Modbus, you should not have this issue. With the proper DDF installed, you actually choose the DDF when you discover the device so as long as the DDF is for that device and is written properly, there is no way the system will auto-select the wrong DDF for you. I did see one that responder note that he had similar issues with a Modbus DDF so that is likely the issue, either the wrong DDF or the DDF was reading improper registers or formatting them incorrectly.


Steve

(CID:105470052)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

In response to DCIM_Support
0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

Hi Steven Thanks for the information, and send mail to multivendorsupport@apcc.com to request the DDF file for my team. Regards

(CID:105470060)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2024-04-09 12:35 AM

Hi 

Im have the same problem a year ago and Schneider  has not been able to answer it yet

(CID:110794297)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2023-10-31 11:30 PM

0 Likes
0
1076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:29 AM . Last Modified: ‎2023-10-31 11:30 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of