Problem with MODBUS devices timeouts on DCE 7.2.4-7.2.6

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Problem with MODBUS devices timeouts on DCE 7.2.4-7.2.6
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:37 AM . Last Modified: ‎2024-04-10 12:49 AM

0 Likes
10
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:37 AM . Last Modified: ‎2024-04-10 12:49 AM

Problem with MODBUS devices timeouts on DCE 7.2.4-7.2.6

Hi all,

I did upgrade DCE from 7.2.0 to  7.2.6. I have a problem with timeouts on  MODBUS devices (Modbus links with EGX300 and 2-8 PM710). Problem occurs from version 7.2.4.

Timeouts on version 7.2.0: max. 1 per day on Modbus link with EGX300 and 8 PM710
Timeouts on version 7.2.6 (7.2.4): 20-30 per day on Modbus link with EGX300 and 8 PM710

The problem also occurs on gateway MOXA.

(CID:93915332)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

0 Likes
5
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

Hello Tomastsk,

 

I am not aware of any changes to DCE in regrades to Modbus TCP communication. Prior to downgrading the server, I would recommend gathering a packet capture to investigate the communication between the two devices. Two packet would be preferred, one closest to the DCE server and the other closest to the EGX300. With both packet capture we can investigate End to End communication. Once the packet capture is gathered please contact your local technical support, here in the North American the technical support phone number is 877-908-2688. By contacting technical support we can create a case to track progress of the issue and escalate this concern to the proper channels.  

(CID:94601855)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:37 AM . Last Modified: ‎2024-04-10 12:49 AM

0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:37 AM . Last Modified: ‎2024-04-10 12:49 AM

Hi Tomas, we will investigate it, thanks for posting!

(CID:94601252)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:37 AM . Last Modified: ‎2024-04-10 12:49 AM

0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:37 AM . Last Modified: ‎2024-04-10 12:49 AM

Hi Piotr, Is possible to do downgrade from 7.2.6 to 7.2.1.

(CID:94601256)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

It is to my understanding only possible to downgrade by reinstalling the old version and the restoring the old backup onto that install. I have no experience trying to restore a newer backup in an older system and it is not recommended. So it is a known issue (since 7.2.4) you are experiencing?

(CID:94601387)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

0 Likes
5
900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

Hello Tomastsk,

 

I am not aware of any changes to DCE in regrades to Modbus TCP communication. Prior to downgrading the server, I would recommend gathering a packet capture to investigate the communication between the two devices. Two packet would be preferred, one closest to the DCE server and the other closest to the EGX300. With both packet capture we can investigate End to End communication. Once the packet capture is gathered please contact your local technical support, here in the North American the technical support phone number is 877-908-2688. By contacting technical support we can create a case to track progress of the issue and escalate this concern to the proper channels.  

(CID:94601855)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

In response to DCIM_Support
0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

I have installed about 10 server (8x BASIC, 1x STANDARD, 1x Virtual) in different sites and customers. Sites with firmware 7.2.0 or 7.2.1 don't have problem with timeots on MODBUS (all timeots are on RS485 sides). One site I upgrade form 7.2.0 to 7.2.6 and next I downgrade to 7.2.0: - before upgrade (7.2.0) - max 1 timeouts per day (timeots on RS485 side) - after upgrade (7.2.6) - about 150 timeouts per day (on 28 MODBUS devices, all PM710) - after downgrade (7.2.0) - no timeots during 1 day from downgrade - I did not change the device settings, hardware, network settings or any settings The problem not cause a change to the MODBUS TCP communication, but a change in the Linux operating system or JAVA (security updates).

(CID:94601872)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

In response to DCIM_Support
0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

Problem occurs on 2 different sites with AP9645 and also other site with AP94VMACT on VMWare.

(CID:94601875)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

In response to DCIM_Support
0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

We would be happy to investigate this issue. We will need a packet capture and the capture logs from the server to start the investigation. Is this something that we could gather?

(CID:94601876)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

In response to DCIM_Support
0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

Please, could you give me your e-mail? I will send you a links (with saved capture logs).

(CID:94601877)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

In response to DCIM_Support
0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2024-04-10 12:49 AM

Please email the links to dcim.tech.support@schneider-electric.com

(CID:94601879)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2023-10-31 11:31 PM

0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:38 AM . Last Modified: ‎2023-10-31 11:31 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now