Hi all,
I did upgrade DCE from 7.2.0 to 7.2.6. I have a problem with timeouts on MODBUS devices (Modbus links with EGX300 and 2-8 PM710). Problem occurs from version 7.2.4.
Timeouts on version 7.2.0: max. 1 per day on Modbus link with EGX300 and 8 PM710
Timeouts on version 7.2.6 (7.2.4): 20-30 per day on Modbus link with EGX300 and 8 PM710
The problem also occurs on gateway MOXA.
(CID:93915332)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
Hello Tomastsk,
I am not aware of any changes to DCE in regrades to Modbus TCP communication. Prior to downgrading the server, I would recommend gathering a packet capture to investigate the communication between the two devices. Two packet would be preferred, one closest to the DCE server and the other closest to the EGX300. With both packet capture we can investigate End to End communication. Once the packet capture is gathered please contact your local technical support, here in the North American the technical support phone number is 877-908-2688. By contacting technical support we can create a case to track progress of the issue and escalate this concern to the proper channels.
(CID:94601855)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:37 AM . Last Modified: 2024-04-10 12:49 AM
Hi Tomas, we will investigate it, thanks for posting!
(CID:94601252)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:37 AM . Last Modified: 2024-04-10 12:49 AM
Hi Piotr, Is possible to do downgrade from 7.2.6 to 7.2.1.
(CID:94601256)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
It is to my understanding only possible to downgrade by reinstalling the old version and the restoring the old backup onto that install. I have no experience trying to restore a newer backup in an older system and it is not recommended. So it is a known issue (since 7.2.4) you are experiencing?
(CID:94601387)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
Hello Tomastsk,
I am not aware of any changes to DCE in regrades to Modbus TCP communication. Prior to downgrading the server, I would recommend gathering a packet capture to investigate the communication between the two devices. Two packet would be preferred, one closest to the DCE server and the other closest to the EGX300. With both packet capture we can investigate End to End communication. Once the packet capture is gathered please contact your local technical support, here in the North American the technical support phone number is 877-908-2688. By contacting technical support we can create a case to track progress of the issue and escalate this concern to the proper channels.
(CID:94601855)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
I have installed about 10 server (8x BASIC, 1x STANDARD, 1x Virtual) in different sites and customers. Sites with firmware 7.2.0 or 7.2.1 don't have problem with timeots on MODBUS (all timeots are on RS485 sides). One site I upgrade form 7.2.0 to 7.2.6 and next I downgrade to 7.2.0: - before upgrade (7.2.0) - max 1 timeouts per day (timeots on RS485 side) - after upgrade (7.2.6) - about 150 timeouts per day (on 28 MODBUS devices, all PM710) - after downgrade (7.2.0) - no timeots during 1 day from downgrade - I did not change the device settings, hardware, network settings or any settings The problem not cause a change to the MODBUS TCP communication, but a change in the Linux operating system or JAVA (security updates).
(CID:94601872)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
Problem occurs on 2 different sites with AP9645 and also other site with AP94VMACT on VMWare.
(CID:94601875)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
We would be happy to investigate this issue. We will need a packet capture and the capture logs from the server to start the investigation. Is this something that we could gather?
(CID:94601876)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
Please, could you give me your e-mail? I will send you a links (with saved capture logs).
(CID:94601877)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2024-04-10 12:49 AM
Please email the links to dcim.tech.support@schneider-electric.com
(CID:94601879)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:38 AM . Last Modified: 2023-10-31 11:31 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.