EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:12 PM . Last Modified: β2024-04-03 11:34 PM
Hello,
My configuration DCE 7.5.0 in virtual machine environment
Public and Private network activated.
My problem is when i am connected with my PC on the private network, when i double click on different type of elements like Raritan PDU or WIB Stulz Web interface, I get in a first stage the Web page of the element (which is correct), but after having typed the password of the element to go further,
when i reach directly from a web browser the elements with their private ip address, it works very well.
It looks like the DCE redirection in private network does not work. Below my network configuration.
Help needed because i have this problem for many clients (also in physical DCE appliance).
Many thanks. Bertrand
DCE public address is 64.2
DCE private A address is 62.2 with mask 255.255.254.0
My PC with DCE client is 62.100 same mask and gateway is 62.2
My raritan PDU is 63.125 with same mask and same gateway than my PC
My WIB Stulz is 63.190 with same mask and sane gateway than py PC
(CID:137110040)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:12 PM . Last Modified: β2024-04-03 11:33 PM
Dear BERTRAND DEPLANQUE ,
Unfortunately, this problem is not yet solved. This problem is inherent for web-GUI 3rd party devices (not native =SE= devices with some exceptions).
You can read more about this issue in topic . In addition, here is Steven Marchetti comment on this:
What happens is the device tries to run a script or launch an active-x or other type of control. The proxy wonβt allow this, not even for NetBotz appliances. Advanced View just uses HTTP or HTTPS so nothing is blocked there.
spezialist is correct that there are a number of people that have entered feature requests but Iβm unsure anything will be recoded for this issue until DCE is totally rewritten. 7.x will likely always have this issue. The alternatives if you must see the device page are to put a laptop on the private LAN or put the device on the public LAN.
If you have more questions, please ask.
With respect.
(CID:137110277)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:12 PM . Last Modified: β2024-04-03 11:33 PM
Dear BERTRAND DEPLANQUE ,
Please tell us if you could solve your question or not?
With respect.
(CID:137729870)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:12 PM . Last Modified: β2023-10-22 03:38 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.