Hi!
I have some recommendations for power equipment.
First says "The measured load exceeds the estimated load per phase designed for the rack". What does it mean?
Settings for capacity group:
Second: The breaker configuration in the Power distribution properties does not match the measured power data (1).
I have no idea what it means.
Third: "Breaker configuration does not support rack's estimated load".
There are two 22 kW rPDU in rack, connected to 32A 3P circuit breaker, and tstimated load is 6.9 kW, failover load - 14 kw. Whats wrong?
How to fix that issues?
(CID:100340784)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:09 PM . Last Modified: 2024-04-09 03:57 AM
Hi Valentin,
Please try as suggested here:
The Measured Load of the UPS Exceeds the Total Estimated Load of the Connected Equipment
(CID:100340794)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:09 PM . Last Modified: 2024-04-09 03:57 AM
Hi Valentin,
Please see the following page:
The Measured Load Exceeds the Estimated Load per Phase Designed for the Rack
(CID:100340797)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:09 PM . Last Modified: 2024-04-09 03:57 AM
Thanks Jef! It's a very strange behavior... I remove phase connection and recommendation is gone.
(CID:100340805)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:09 PM . Last Modified: 2024-04-09 03:57 AM
Change from L3 to L1
(CID:100340806)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:09 PM . Last Modified: 2024-04-09 03:57 AM
And what about "The breaker configuration in the Power distribution properties does not match the measured power data"?
I cant find description.
(CID:100340868)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:10 PM . Last Modified: 2024-04-09 03:57 AM
Hi Valentin, Please see this page: http://dcimsupport.apc.com/display/UAOp74/The+Breaker+Configuration+in+the+Power+Distribution+Proper...
(CID:100340899)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:10 PM . Last Modified: 2023-10-31 11:30 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.