Power Meter and PDU Association

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Power Meter and PDU Association
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

0 Likes
12
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

Power Meter and PDU Association

I have a floor mounted PDU that contains a breaker panel that feed all the rack mounted PDUs.  I have already associated a Power Meter (Power Logic PM710) to the floor PDU, to get the total readings from the unit but I am now unable to associate a rack mounted PDU (via DCE) to it in order to do sensor mapping so I can have reading at the rack level.

 

Is this a known issue?

 

 

(CID:106203242)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

0 Likes
2
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

you need to associate your DCE rack mounted pdu to its corresponding rack pdu in the rack.  You can do this by clicking the rack in the floor layout and dragging the rack pdu from the unassociated devices window onto the rack pdu in the rack view.  You could also drag it onto the rack pdu in the navigation window.

 

Also for future refernce, you don't have to create the rack pdu first in DCO, you can drag the rack pdu straight from unasssocaited devices right into the rack.

(CID:106203253)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

Andrew Trabert I have tried this but the measurements that are returned when associating the device are incorrect. I had spoken to Multi Vendor Support and they suggested the sensor mapping route

(CID:106203254)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

sorry that I didn't realize you were trying to do sensor mapping. Here's a link on how to do it https://dcimsupport.apc.com/display/public/UAOp74/Configuring+Branch+Circuit+Monitoring you should be able to right click the pdu in the floor layout and choose sensor mapping as an option. out of curiosity, are these rack pdus daisy chained together so that they share an IP (eg 1 device in DCE has power output for multiple rack pdus?)

(CID:106203311)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

0 Likes
7
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

Hi @james.halpin

If you have metered rack mount pdu's then you should be able to have the measured data at the rack level by putting(or associating) the rack mount PDU's into the racks. If you get the wrong values from the rack PDU's when doing that it indicates that the Device Definition File (DDF ) is not returning the right values. 

What type of rack PDU's are you using? Knowing that,  I'll have a representative from our DDF team reach out to you and work through the issues that you are experiencing.

The sensor mapping solution is only a workaround - and we should fix the underlying issue. I'm sorry that we sent you off in the wrong direction (from Multi Vendor Support) but I'm sure that we will be able to work with and resolve the issue.

Best Regards

Anders

(CID:106203546)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:30 AM . Last Modified: ‎2024-04-09 12:16 AM

Anders Thorbjørn Jensen The issue is with Geist rack PDUs. There are two different types (and two DDFs), the ones using the Geist IMDPDU DDF work fine (by associating them to the rack PDU in DCO) however the Geist Quantal Legacy PDU DDF is the one I am having issues with. I can provide screen shots and more information to the DDF team.

(CID:106203614)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

are any of your geist pdus daisy chained in a master/slave configuration and share an ip? or do they all have their own ip? unless i'm mistaken, the master/slave configuration would require you to use the sensor mapping work around since I don't know how else you would separate multiple pdus that show up as a single device in DCE.

(CID:106203620)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

All have individual IP addresses

(CID:106203649)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

Hi @james.halpin The latest version of the DDF "geist_quantal_legacypdu.xml" is version 8 and I am attaching it to this comment. In case if the attached DDF did not work as well, please send us a WALK file of the device by running the walk utility by following the instructions given in the following link "http://www.apc.com/support/index?page=content&country=ITB〈=EN&locale=en_US&id=FA158391";. Please do attach any MIB files you have for this particular device.

(CID:106203660)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:16 AM

Mohan Gowda G S I have removed your comment. Please, do not disclose personal details (ex. e-mails) of a customer.

(CID:106203682)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:15 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:15 AM

@james halpin After investigation this issue, We came to know that one particular DDF present in your DCE central is causing this issue. I have now rectified the problem and made the necessary change in the DDF file. Can you please delete the DDF with DDF name "Hawk-i2" from your DCE server and add the latest version of it (Version 11). You can find the latest version of the DDF file in the below link. https://schneider-electric.box.com/s/u42nedxo241j5eynf5imtt7qigsm50zq The results were tested in SoapUI and I got values for all the 3 phases.

(CID:106204226)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:15 AM

In response to DCIM_Support
0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2024-04-09 12:15 AM

Punith Narayanagowda I have updated the DDF and the values are coming through now. Thanks for the assistance

(CID:106204250)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2023-10-31 11:30 PM

0 Likes
0
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:31 AM . Last Modified: ‎2023-10-31 11:30 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of