PUE data is not reflecting on Web Portal ?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • PUE data is not reflecting on Web Portal ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:56 PM . Last Modified: ‎2024-04-09 04:01 AM

0 Likes
8
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:56 PM . Last Modified: ‎2024-04-09 04:01 AM

PUE data is not reflecting on Web Portal ?

(CID:100340343)

Labels
  • Labels:
  • Portal
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

Hi Santosh, Could you please explain a little more in detail which PUE is not updating and where. Is it the "PUE Dashboard", "Energy Efficiency" or the Struxureware Portal that is being used? /Søren

(CID:100340356)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

Hi Santosh,

 

After rethinking I'm pretty sure what you mean is that the PUE seen in the Struxureware Portal is not the same as seen in the DCO server dashboard.

This is something that has been discused earlier here: 

Please be aware that the PUE in the KPI ticker and KPI portlet are showing the daily KPI value for PUE and not a "live" PUE value.

 

/Søren

(CID:100340492)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

0 Likes
4
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

Hi Santosh,

I believe we had checked this issue for your site and found out, you are not using Energy Efficiency Module for displaying PUE and you wanted to display the PUE dial in Portal using the Portlet which requires EE system. To display the Instantaneous PUE you can use the Iframe object and place the same into Portal, I had mailed you the snapshot of the same as well, that will resolve your pending concern.

(CID:100340721)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

In response to DCIM_Support
0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

Vineet K. Sarin Are you able to forward the details on? I have a similar situation where I have the raw data for calculating PUE but no way of doing the division between two sensor points and displaying in DCE, Portal or DCO (without it being a state wide value)

(CID:100340804)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

In response to DCIM_Support
0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

Hi James with the case for Santosh he never had EE installed but had the Capacity module and Operations to atleast display the PUE there. So the only part he wanted was to display that dashboard inside Portal, which can be easily done using iframe. If in case you are targeting custom field creation like taking into account two variables and adding, multiplying etc and then displaying them somewhere then you have to use XML programming and there are better custom portlets for liferay which can help you do that faster...

(CID:100340855)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

In response to DCIM_Support
0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:01 AM

Vineet K. Sarin Not having delved into the Liferay portlet world, do you know if there is a portlet that can take two values (DCE sensor values) and apply a mathematical equation to them?

(CID:100340896)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:00 AM

In response to DCIM_Support
0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2024-04-09 04:00 AM

Hi James there is a Portlet which you can use, see the following website and that can give you many ideas...http://xmlportletfactory.org/ Also if you are well versed with XML scripts or Web programming then you can use the Web content Portlet available inside the Portal to create enriched webpages that can accept values from different variables.

(CID:100340927)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2023-10-31 11:31 PM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:57 PM . Last Modified: ‎2023-10-31 11:31 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore