POE Repeater

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • POE Repeater
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:07 PM . Last Modified: ‎2024-04-03 12:14 AM

0 Likes
9
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:07 PM . Last Modified: ‎2024-04-03 12:14 AM

POE Repeater

We have a netbotz appliance 450 and netbotz pod 150. we want to connect them through A-link port using Ethernet cat-5 cable. and the length between them is 107 meters so we need to use a POE repeater. so we need a recommendation for a repeater? or other solution if there?

(CID:151060957)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:07 PM . Last Modified: ‎2024-04-03 12:14 AM

0 Likes
7
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:07 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi Mohamed,

It's not ethernet so I wouldn't use a POE injector. The sensor pod 150 has a power jack on it and we suggest using the AP9595I power supply.

 

Steve

(CID:151060973)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

In response to DCIM_Support
0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi Steve,

let me clarify the issue. we have 2 netbotz, the distance between them is 107 meters and we need to connect them and the netbotz pod 150 installed in a place does not have power source. so we are not able to use a power supply for netbotz 150. it will take the power from netbotz 450 (POE). so what is your recommendation? and
is 107 meters are OK and we do not need to use a repeater to extend the length?

(CID:151060985)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

In response to DCIM_Support
0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi Mohamed,,


From a single NetBotz appliance to a single pod, 107 meters should be OK without power. As I mentioned, a POE injector is for ethernet and the pinouts (sorry, I can't provide them) for A-link do  not match up. That being the case, the pod or maybe even the appliance could be damaged. 


Steve

(CID:151061006)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

In response to DCIM_Support
0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi Steve,

As i understand from you, I do not need to use a POE repeater/injector as the distance of 107 meters is OK and the sensor pod-150 will be directly supplied with power via POE (A-link of NetBotz-450). is that right?

So, What is the max. allowable node to node distance for A-link?

 

(CID:151061044)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

In response to DCIM_Support
0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi Mohamed,

 The Alink protocol has a maximum distance of 1000 meters (3,280 ft). Connected via Cat5 cabling which has a functional limitation of 100m per length. I believe an extra 9 meters will not cause an issue.


Yes, the pod will be powered by the unit itself. Since you mentioned using the 450, that unit is powered by AC and not POE. If you are instead using the wall mount 455, that is powered by POE. In either case, there is enough power for the 2 pods.


Steve

(CID:151061069)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

In response to DCIM_Support
0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi Steve,

In case of the distance reach 130 meters what is your recommendation for that ?

(CID:151061128)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

In response to DCIM_Support
0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi Mohamed,


I've provided the specs and the recommended alternate power options. An extra few meters should not matter. Again, this is a cat5 limitation (100 meters per length) and you could end up with comm issues at these distances. I can't promise that in your environment it will work. I can't say that it won't. Every environment is different. I'll assume that in a perfect world, 130 meters for an individual length would still work but I can't make any promises. I can only provide the info I've already provided. 

(CID:151061152)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

In response to DCIM_Support
0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2024-04-03 12:14 AM

Hi steve,

Thank you for your support.

(CID:151061282)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2023-10-22 03:31 AM

0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:08 PM . Last Modified: ‎2023-10-22 03:31 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore