No readings from Netbotz 550 internal sensor pod

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • No readings from Netbotz 550 internal sensor pod
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Anonymous user
Not applicable

Posted: ‎2021-04-16 04:39 PM . Last Modified: ‎2021-04-26 03:25 AM

0 Likes
9
1892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-16 04:39 PM . Last Modified: ‎2021-04-26 03:25 AM

No readings from Netbotz 550 internal sensor pod

Hello to everyone!

 

I would like to, please, have some of your help about the situation that I presently have with my netbotz 550:

 

Everything was working fine, but we had to move from one building to another, and so the netbotz got relocated too. When it was conected on the new room it still could read info (3 parameters) from the external sensor (conected via A-LINK) but the internal sensor showed up error condition on the three reading parameters (temperature, humidity and dew point).

 

On the Advanced View software the only option that I had, was to delete the sensor/parameters, so I deleted it, expecting that the connection could be reestablished after a reboot. But unfortunately that did not happened, now I get absolutely nothing, not even an error condition, as you could see on the two images of below: on the external sensor I get readings (3 parameters) but on the internal I get absolutely nothing.

 

ScreenShot.png

 

Could the internal sensor be dead? But if he's dead I guess this should trigger some kind of error condition, right? (I don't have any error on my netbotz 550, only the abscence of parameters from the internal pod)

 

Is there any procedure that could be done to regain readings from the internal sensor?

 

Any help would be appreciated!

 

Thanks in advance!

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
spezialist
Commander spezialist
Commander

Posted: ‎2021-04-16 10:52 PM

0 Likes
8
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-16 10:52 PM

Dear @Anonymous user,

 

First of all, in such a case, I highly recommend that you unconfig the device without resetting the network settings (can be done remotely): http://your_netbotz_address/unconfig .

This is e.g. described in =SE= FA234703 and I also wrote about it in post NetBotz 4.x: how to remove non-existent sensors from AV, with N/A readings? time ago.

Try it, I hope it helps you.

 

Regards.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-19 05:33 AM . Last Modified: ‎2021-04-19 09:48 AM

In response to spezialist
0 Likes
7
1873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-19 05:33 AM . Last Modified: ‎2021-04-19 09:48 AM

Hello @spezialist , 

 

Firstly let me thank you for your assistance!

 

I did exactly what you recomended, on saturday night, the device booted up, the problem still occurs, but the netbotz was working. I started check configurations once more, and suddenly the netbotz stopped responding. I was working remotely, so only today I got near the netbotz for further investigations.

 

Today, I firstly removed power, reconnect the power cable, still nothing...it did not respond...

 

Tried RESET button on the device, but nothing...it still did not respond when I tried to connect via LAN port.

 

I removed netbotz from the room where it was, connected it through usb console port, tried to do a full reset (via command line I used the CONFIGRESET command). Apparently the procedure went well, but when netbotz restarts I see on the end of boot procedure, on terminal screen the following error:

 

Kernel panic - not syncing: Must restart system to assure recovery

 

After 5 seconds the device reboots and it starts over again, until the same error occurs, and the netbotz is on a infinite loop...

 

Any further help, please?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

spezialist
Commander spezialist
Commander

Posted: ‎2021-04-19 10:45 AM

In response to Anonymous user
0 Likes
6
1856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-19 10:45 AM

Dear @Anonymous user ,

 

It looks like a hardware malfunction, unfortunately :-(. I can only recommend you to search similar threads here (netbotz loop booting) with a possible solution to the problem. Also look towards =SE= FA176133, e.g. "NetBotz TFTP upgrade/recovery procedure".

 

I hope this helps you.
With respect.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-20 05:36 AM

In response to spezialist
0 Likes
5
1840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-20 05:36 AM

Hello @spezialist , thanks again for your help!

 

I already made the upload of firmware (tried version 4.6.2 and even 4.6.1) but the problem persists...the Kernel panic message occurs and netbotz reboots...and the endless loop begins...

 

I've checked all the messages I get on terminal screen during the boot process and I was alerted by the following two:

....

....

....

VFS: Mounted root (jffs2 filesystem) readonly.
Freeing unused kernel memory: 100k init
Jan 1 00:15:43 modprobe: FATAL: Could not load /lib/modules/2.6.12/modules.dep: No such file or directory

Jan 1 00:15:43 modprobe: FATAL: Could not load /lib/modules/2.6.12/modules.dep: No such file or directory

INIT: version 2.83 booting
Checking all file systems...
fsck 1.38 (30-Jun-2005)

....

....

 

I guess those messages should not occur...what could they mean?

 

I also opened up the chassis and I have a bulging capacitor on the power supply, could this be the problem? (but I checked the output of power supply and I got 24 Volts)

 

Any further ideas?

 

Thanks in advance

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

spezialist
Commander spezialist
Commander

Posted: ‎2021-04-20 06:37 AM . Last Modified: ‎2022-10-19 01:45 AM

In response to Anonymous user
0 Likes
4
1838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-20 06:37 AM . Last Modified: ‎2022-10-19 01:45 AM

Dear @netbotz,

 

 


@netbotz wrote:

I also opened up the chassis and I have a bulging capacitor on the power supply, could this be the problem? (but I checked the output of power supply and I got 24 Volts)

Quite right, your NetBotz has been powerd up for a very long time and some of its radio components are now faulty. This is the reason why the device's firmware is corrupted.

Of course you can try to replace the defective radio parts. And only then try to reflash the NetBotz with the latest firmware version. Version 4.6.4 is officially available for download. However, new devices already come with version 4.7.0 (see my post https://community.se.com/t5/EcoStruxure-IT-forum/Where-can-I-download-the-current-version-of-NetBotz...).

 

Try it and maybe it will work for you. I would do so.

 

With respect.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-20 08:51 AM

In response to spezialist
1 Like
3
1832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-20 08:51 AM

Hello again @spezialist ,

 

I already installed the latest firmware that you kindly suggested, but unfortunately the problem still occurs.

 

On the next few days I will try to buy, and then replace, the bulging capacitor so I could then report here what happened. As soon as I finish this procedure, I will post here a new message.

 

Thanks again for all your help!

 

Best regards

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-22 05:40 AM

In response to Anonymous user
0 Likes
2
1819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-22 05:40 AM

Hello again @spezialist ,

 

I changed the capacitor but the problem still occurs the exact same way. As last resort I've been trying some commands, and I used the command "eraseflash all", the procedure was made, and now the device is absolutey dead, no boot at all. Is there any other way to rewrite the firmware again?

 

Thanks in advance.

 

Best regards.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

spezialist
Commander spezialist
Commander

Posted: ‎2021-04-24 09:27 AM

In response to Anonymous user
0 Likes
1
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-24 09:27 AM

Dear @Anonymous user,

 

Unfortunately, it is difficult for me to recommend anything else in this case: I have never used the "eraseflash all" command in my practice for obvious reasons. I need some time, maybe I will find something really useful for this situation.

 

With respect.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-26 03:23 AM

In response to spezialist
0 Likes
0
1733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-26 03:23 AM

Hello @spezialist ,

 

Well...thanks a lot for the simple thought that you will think about my problem... and try to find some way to fix it.

 

Obviously, I will wait...it's the only thing I could wisely do...

 

Thanks again!

 

Best regards!

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of