I had a Netbotz 13.56 rack access control in a project and it has 2 A-link port and i have 2 temp/humidity sensors with display can i connect each one on a port or as the manual shows one port should has a terminator while the other can connects to the 2 sensors cascaded ?
(CID:152080479)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:55 PM . Last Modified: 2024-04-02 11:45 PM
Dear Islam Fouad Elkholy,
A-Link ports of NetBotz devices are absolutely equal and identical. Therefore, all three connection methods are correct and can be applied:
Term->ALnk|NetBotz|ALnk<---->ALnk|TH1|ALnk<---->ALnk|TH2|ALnk<-Term
Term->ALnk|TH2|ALnk<---->ALnk|NetBotz|ALnk<---->ALnk|TH1|ALnk<-Term
Term->ALnk|TH2|ALnk<---->ALnk|TH1|ALnk<---->ALnk|NetBotz|ALnk<-Term
The basic rule of the A-Link bus, as for similar serial data buses, is the use of terminators (wave impedance balancers of the communication line) at both ends of the communication line.
With respect.
(CID:152080515)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:55 PM . Last Modified: 2024-04-02 11:45 PM
Dear Islam Fouad Elkholy,
A-Link ports of NetBotz devices are absolutely equal and identical. Therefore, all three connection methods are correct and can be applied:
Term->ALnk|NetBotz|ALnk<---->ALnk|TH1|ALnk<---->ALnk|TH2|ALnk<-Term
Term->ALnk|TH2|ALnk<---->ALnk|NetBotz|ALnk<---->ALnk|TH1|ALnk<-Term
Term->ALnk|TH2|ALnk<---->ALnk|TH1|ALnk<---->ALnk|NetBotz|ALnk<-Term
The basic rule of the A-Link bus, as for similar serial data buses, is the use of terminators (wave impedance balancers of the communication line) at both ends of the communication line.
With respect.
(CID:152080515)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:56 PM . Last Modified: 2024-04-02 11:45 PM
thank you for you assistance
(CID:152080529)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:56 PM . Last Modified: 2024-04-02 11:45 PM
Ok, very thanks for the good feedback 😀.
(CID:152080531)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 11:56 PM . Last Modified: 2023-10-22 03:23 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.