Posted: 2025-05-09 05:56 AM
We have about 30 755's up and running now.
A few have Camera Disconnected alarms from the installation time. All the cameras are working, communication between the netbotz and camera is working. DCE is happily talking to the netbotz, and getting the camera feed.
But permanently got the alarm showing both in DCE and in the 755 web interface. These are remote devices, already bolted to ceilings.
Is there another way to reset the alarm through the webinterface or by SSH magic?
If there's already a documented/known way of resetting the alarm within Linux, before I go exploring...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-24 08:13 AM
Restting the password on the camera, then letting the netbotz "lose" it, then doing a "fix credentials" clears the alarms.
A clear alarm button maybe useful 😉
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-12 05:56 AM
Hi @Lincoln_Darran,
For faster resolution, you may want to contact your local technical support for help with this issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-24 08:13 AM
Restting the password on the camera, then letting the netbotz "lose" it, then doing a "fix credentials" clears the alarms.
A clear alarm button maybe useful 😉
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of