Netbotz 755 DHCP hostname

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz 755 DHCP hostname
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Lincoln_Darran
Lieutenant JG Lincoln_Darran
Lieutenant JG

Posted: ‎2024-10-17 05:38 AM

0 Likes
8
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-17 05:38 AM

Netbotz 755 DHCP hostname

Afternoon Supporters,

 

We've recently refreshed a lot of our Netbotz estate and moved from 355s to 755s.

 

Got them all running 5.4.0.11, most things I've worked out and got working.

 

However, keep getting dns info being stomped all over by the devices registering in DHCP as snarc-soca9

 

Hostname is configured on all the devices, but on DHCP refresh they change to snarc-soca with a "strange" MAC address. Screenshot 2024-10-17 133321.png

 

Anyone found a work around or fix?

 

Darran

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Cory_McDonald
Admiral Cory_McDonald Admiral
Admiral

Posted: ‎2024-10-28 07:02 AM

0 Likes
1
1339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-28 07:02 AM

Hello @Lincoln_Darran,

 

I recommend reaching out to technical support to look into this issue further.  I have also reached out to some people internally within Schneider to see if I can get more guidance on this, but getting something officially logged through support should help move this issue along for you.

 

If I hear anything back, I'll ensure to reach out, but I still recommend you reach out to support.

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lieutenant JG Lincoln_Darran
Lieutenant JG

Posted: ‎2024-10-28 07:05 AM

In response to Cory_McDonald
0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-28 07:05 AM

@Cory_McDonald thanks for kepeing a watch on the thread.

 

I've got an open ticket with support for this.

 

I'll post once I've got something back 🙂

 

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2024-10-28 09:03 AM

0 Likes
1
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-28 09:03 AM

Hi @Lincoln_Darran ,

I spoke with engineering on this and I believe there is also a case opened on this with a rep. I've told them the same thing as I'll write here to you.
Engineering believes we're going by the RFC for this but they're still looking into how they might make it easier for you. This may take time however and you'll definitely run into this issue multiple times before and if this is addressed.
Engineering suggested that you create DHCP reservations for these devices and they feel that will resolve the issue. Assuming you're also the one that opened the case with the rep, I'll ask that any future correspondence on this issue take place there as this forum is not monitored as thoroughly.

Thanks,
Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lieutenant JG Lincoln_Darran
Lieutenant JG

Posted: ‎2024-10-28 09:14 AM

In response to APC_Steve
0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-28 09:14 AM

Hi @APC_Steve 

 

Yep, I have a case open.

 

Tried DHCP reservations, to no effect.  Think it's down to interpretation of the DHCP RFCs.  Noticed that the newer UPS NMCs are also starting to use what looks like the same kernel as the 755s, and they're not honouring the domain name in the DHCP negotiations.

 

I realise the M$ DHCP implementation isn't the best, but it does seem a common issue with device using newer linux distros with a DHCP client enabled.

 

Thanks for your help

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2024-10-29 04:12 AM

0 Likes
0
1309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-29 04:12 AM

Hi @Lincoln_Darran ,

I've noted your comments in the engineering log for this. Hopefully it helps.

 

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

joshellisSE
joshellisSE Cadet
Cadet

Posted: ‎2024-11-06 10:55 AM

0 Likes
1
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-06 10:55 AM

Hello @Lincoln_Darran , which UPS NMC's are you noticing this with?  You mentioned that they're using the same kernel as the Netbotz 750 so I'm going to assume you're referring to the NMC4, used in our Galaxy VS/VL UPS line?   Does that sound correct?

Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lieutenant JG Lincoln_Darran
Lieutenant JG

Posted: ‎2024-11-07 02:00 AM

In response to joshellisSE
0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-07 02:00 AM

Hi @joshellisSE 

 

I don't have any real evidence of a common kernel.  Just a a feeling of how both devices operate.  

 

And yes, it is the NMC4 cards I was talking about, in Galaxy VS's.

 

HTH

Reply

Link copied. Please paste this link to share this article on your social media post.

Lincoln_Darran
Lieutenant JG Lincoln_Darran
Lieutenant JG

Posted: ‎2025-03-21 03:14 AM

0 Likes
0
633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-21 03:14 AM

Think I might have solved it!

 

For some reason the snarc-soca9 hostname is used against the 127.0.1.1 interface, which somehow gets pushed out over the public interface during the DHCP process. Strange behaviour.

 

Anyway, login as root over ssh. edit /etc/hosts and insert the "real" hostname in front of snarc-soca9 on the 127.0.1.1 host record line. as below

 

127.0.1.1    MyRealHostname snarc-soca9

 

Use the reboot command to make that the live config, and those pesky snarc-soca9 records will slowly TTL out of your dhcp/dns.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of