Why is there no SNMPv2 Counter64 support in DCE?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Why is there no SNMPv2 Counter64 support in DCE?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
OmerHanay
Ensign OmerHanay
Ensign

Posted: ‎2025-03-13 01:44 AM

0 Likes
3
406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-13 01:44 AM

Why is there no SNMPv2 Counter64 support in DCE?

I need to read Counter64 values using SNMPv2, but in the web interface, only SNMPv1 and SNMPv3 are available. Even though SNMPv2 is supported, Counter64 values cannot be read.

The product I want to integrate broadcasts certain SNMPv2 data points using Counter64. How can I resolve this issue?

 

MIB BROWSER Walk;

 

1.3.6.1.4.1.35483.1.1.1.3.1.1.3.290, OctetString , Modbus-Temp-Hum.Temperature3
1.3.6.1.4.1.35483.1.1.1.3.1.1.3.291, OctetString , Modbus-Temp-Hum.Humidity3
1.3.6.1.4.1.35483.1.1.1.3.1.1.3.292, OctetString , Modbus-Temp-Hum.Temperature4
1.3.6.1.4.1.35483.1.1.1.3.1.1.3.293, OctetString , Modbus-Temp-Hum.Humidity4
1.3.6.1.4.1.35483.1.1.1.3.1.1.4.0, Counter64 , 2311
1.3.6.1.4.1.35483.1.1.1.3.1.1.4.1, Counter64 , 0
1.3.6.1.4.1.35483.1.1.1.3.1.1.4.2, Counter64 , 5000
1.3.6.1.4.1.35483.1.1.1.3.1.1.4.3, Counter64 , 1000
1.3.6.1.4.1.35483.1.1.1.3.1.1.4.4, Counter64 , 0
1.3.6.1.4.1.35483.1.1.1.3.1.1.4.5, Counter64 , 0

 

DCE Web Snmp Walk;

 

2025-03-13_11h43_25.png

 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
OmerHanay
Ensign OmerHanay
Ensign

Posted: ‎2025-03-22 02:41 PM

In response to APC_Steve
2 Likes
0
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-22 02:41 PM

Yes the problem was solved when we used SNMPv3. Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2025-03-14 04:29 AM

0 Likes
0
362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-14 04:29 AM

Hi @OmerHanay ,

 

I see that SNMPv1 does not support the counter64 data type but in reading up on SNMPv3, it should support the counter64. Was your walk only in SNMPV1 or did you try SNMPv3 as well. 


I don't have anything that I know for a fact outputs a counter64 type so I can not test but I would assume that since DCE supports the same data and same DDF files, that the data types supported must remain the same between the 2 supported versions for compatibility reasons. I can try to speak with engineering on this but what I can tell you is that there is no configuration option that can be adjusted in DCE to allow for any data type that it is not already supporting.

 

Tanks,

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2025-03-14 04:36 AM

0 Likes
1
359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-14 04:36 AM

P.S.
Your above walk WAS in SNMPv3, correct?

Reply

Link copied. Please paste this link to share this article on your social media post.

OmerHanay
Ensign OmerHanay
Ensign

Posted: ‎2025-03-22 02:41 PM

In response to APC_Steve
2 Likes
0
278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-22 02:41 PM

Yes the problem was solved when we used SNMPv3. Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of