Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Netbotz 570 and Netbotz 500 connected to same modem

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 570 and Netbotz 500 connected to same modem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:56 AM

0 Likes
6
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:56 AM

Netbotz 570 and Netbotz 500 connected to same modem

Good day

 

Please assist

We have Netbotz 570 and Netbotz 500 connected via USB Hub to a common modem (Multi-tech GSM modem). The USB hub has 4 camera's and 1 modem connected which both appliance use to send SMS. Camera's are all operational. 

All of a sudden I have lost SMS functionality on Netbotz 500 device. I am not receiving SMS alerts from the 500 device. SMS Icon under Strength Tab and Quality Tab display Unknown. I am able to receive SMS from 570 as per norm.

I have verified all physical connections and rebooted the appliance with no success.

Any other options/tricks that I may try ?

Your assistance is very much appreciated.

 

Kind regards

Juice

 

(CID:132671787)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:56 AM

0 Likes
3
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:56 AM

Hello Juice,

 

Did you check tryed to check the logs or if there's an update missing at the netbotz 500?

 

Wich modem model are you using? And wich firmware version you have installed?

(CID:132671815)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:52 AM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:52 AM

Hi there Emenson

Thanks for your assistance. See below logs

I am using the Multi-Tech MultiModem Cell.

Before i start to disconnect cables and appliances or even hubs which will definately affect the Netbotz 570 operations, i asked the group for their expertise.

 

Thanks you thus far.

Juice

(CID:132671841)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:52 AM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:52 AM

Hi Gents

As a matter of interest, I looked at the actual connections of the Netbotz equipment and i do not see any physical connection from the Netbotz 500 (problem) to the modem.

The Netbotz 550 is connected to the modem and cameras via a USB D-Link Hub. (working)

1, is it possible the Netbotz 500 has lost its configuration to the Netbotz 550 and ultimately to the modem? And 2, how would you connect 2x netbotz appliance using 1 modem ? if theres a guide to assist please forward me the link.

Thank you for your assistance.

Juice

 

(CID:133372187)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:52 AM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:09 PM . Last Modified: ‎2024-04-04 03:52 AM

Hi gents... i am still sitting with this problem and i havent yet found a solution. Worst case would be to reformat and reconfigure the 500 device, however, this be the last resort.

Please assist.

(CID:134026160)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:10 PM . Last Modified: ‎2024-04-04 03:52 AM

0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:10 PM . Last Modified: ‎2024-04-04 03:52 AM

Hi Guys... i still need possible solutions....

(CID:133368547)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:10 PM . Last Modified: ‎2023-10-22 03:20 AM

0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:10 PM . Last Modified: ‎2023-10-22 03:20 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore