Netbotz 570 Error on log file

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 570 Error on log file
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

0 Likes
5
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

Netbotz 570 Error on log file

Hi there

I am receiving below error:

For security purposes i removed the IP details;

Currently we not able to retrieve any surveillance clips from DCE however we do receive e-mail snippets (pics) from the appliance.

I have verified all the configs of the appliance and the surveillance settings however still no clips.

Any suggestions?

Background info; Netbotz 500, advance view 4.62, Camera Pod 120, DCE - 7.4.1

 

Regards

Juice

(CID:134026194)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

Hi gamie, thanks for posting!

Let's hope you find your answer here.

Thanks,

Stine

(CID:134029010)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

0 Likes
2
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

gamie,

If you are not using Data Center Expert (DCE), check the following setting:

1) Log into the NetBotz appliance using Advanced View.

2) Click on the Configuration tab (pane).

3) Within Appliance Settings double-click on Data Center Expert (formerly called InfraStruXure Central).  NOTE: This screen may take a minute or two to load.

4) Find the entry that has the type of post "Surveillance" and select it and then select Remove. 

This action should stop the bot from trying to send surveillance images to Data Center Expert.  If the camera is enabled fro surveillance in DCE, these options may re-enable themselves for the posting on images back to DCE.

If the error messages persist after performing the above action, I would recommend reaching out to your local technical support for them to fully investigate.

Kind Regards,

Cory

(CID:134029180)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

In response to DCIM_Support
0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

Hi Cory, I am experiencing the same issue.

I will give this a try. 

I am using DCE 7.4 . Will logon Advance view and remove the surveillance.

Should i need to add it again, how do i go about it? Would the "remove button" become an "add button"?

If there is a "how to doc" please forward the link.

Kind regards

(CID:134029569)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

In response to DCIM_Support
0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2024-04-04 02:48 AM

Once the camera is enabled for surveillance in DCE, the surveillance posting should re-enable itself on the NetBotz Appliance.

(CID:134029703)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2023-10-22 03:20 AM

0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:42 PM . Last Modified: ‎2023-10-22 03:20 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore