Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Adeel_Tahir
Crewman Adeel_Tahir Crewman
Crewman

Posted: ‎2020-10-21 04:46 AM

0 Likes
2
1770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-21 04:46 AM

Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator

Hi,

 

We are offering a Netbotz 250 for a small 2 racks server room. I was wondering if it is possible for the Smoke Sensor to detect smoke and activate the relay output. The relay output will be connected to the actuator supply and it will release the Fire agent. In this way we can eliminate the Fire Alarm Control Panel for this site and save cost. Or if we can use the temperature sensor to do it.

Any suggestions regarding this? Is it workable and safe? Is it recommended?

 

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KevinK
Lieutenant | EcoXpert Master KevinK Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-10-21 05:12 AM

1 Like
0
1762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-21 05:12 AM

Hi @Adeel_Tahir ,

 

It is very possible to have a Netbotz smoke sensor detect smoke and activate the relay output. However, it may be a better idea to connect a dry contact to an existing Building Smoke sensor in the room and have that activate the relay instead. Remember Netbotz Smoke sensor are for installation inside of IT racks. So if this is to extinguish the room it would make sense to integrate into the building smoke sensor in my opinion.

 

Regards

Kevin

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
KevinK
Lieutenant | EcoXpert Master KevinK Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-10-21 05:12 AM

1 Like
0
1763
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-21 05:12 AM

Hi @Adeel_Tahir ,

 

It is very possible to have a Netbotz smoke sensor detect smoke and activate the relay output. However, it may be a better idea to connect a dry contact to an existing Building Smoke sensor in the room and have that activate the relay instead. Remember Netbotz Smoke sensor are for installation inside of IT racks. So if this is to extinguish the room it would make sense to integrate into the building smoke sensor in my opinion.

 

Regards

Kevin

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Andy
Andy Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2020-12-23 01:18 PM

1 Like
0
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-23 01:18 PM

Hello, I believe it's not safe as the product is not a certified fire suppression system and (as I think) it should be even restricted by the local regulations to implement such systems. A possible accident may cost lives. Please ask the person responsible for fire protection on the site. Regards/Andrey

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of