Netbotz 250 SNMPv3 authentication issue

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 250 SNMPv3 authentication issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
12
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

Netbotz 250 SNMPv3 authentication issue

Hello! I've been able to get Netbotz and SNMP to work and can query for basic things such as the name of the device using the net-snmp linux command line tools. This works for both SNMPv1 and SNMPv3 (with no authentication) such as:

 

$ snmpget -v3 -l noAuthNoPriv -u "apc snmp profile2" 192.168.1.20 sysName.0 SNMPv2-MIB::sysName.0 = STRING: apc0D8DA9

 

 

However, when I try to enable authentication (I've tried MD5 and SHA) and set a passphrase, I receive a "Timeout: No Response from 192.168.1.20" error.

 

$ snmpget -v3 -l authNoPriv -u "apc snmp profile2" -a MD5 -A "PASSWORD1234567" 192.168.1.20 sysName.0 Timeout: No Response from 192.168.1.20.

 

I've tried switching profiles, changing MD5 and SHA, changing passwords, etc but so far I've been unsuccessful in getting SNMPv3 authentication working. Firmware version: v6.5.6. SNMPv1 and SNMPv3 are both enabled. In this test above 'apc snmp profile2' is enabled. Any assistance getting authentication working is appreciated!

 

Brian

 

(CID:137109973)

Labels
  • Labels:
  • NetBotz
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
1
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

This issue appears to have been resolved by firmware update 6.6.7.

(CID:137725881)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

Update: I was able to get it to work by setting the passphrases through the web interface instead of through ssh. Does this make any sense? Is there a difference between the web admin interface  vs the ssh interface for configuring SNMP?

Brian

(CID:137110037)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

Dear Brian Hobson,

Thanks for the update.

Can you show a screenshot from ssh CLI and from the web-GUI, as you exactly perform the above configuration of SNMPv3 authentication (this may be important) for NetBotz-250 device.

With respect.

(CID:137110104)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

Sure! The first screenshot shows that profile2 authentication is set to None before I set it to SHA using the ssh interface.

The next screenshot shows that the authentication mechanism has been set to SHA and shows my attempt to query for the system name using snmpget. The request shows a timeout error.

The last screenshot shows how I set the authentication to SHA using the web UI. After doing this, the same snmpget request works as expected.

 

Hope this helps, let me know if you need any further data.

 

Brian

(CID:137110401)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:10 PM . Last Modified: ‎2024-04-03 11:34 PM

Dear Brian Hobson,

Many thanks for the detailed screenshots: this is probably a bug.

I hope that soon the Support team will pay attention to this.

With respect.

(CID:137110422)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

Thanks. Is there a place where I can submit a bug report or are you handling that process?

(CID:137110427)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

Dear Brian Hobson,

Unfortunately, I do not know of such a special resource. Maybe Steven Marchetti or Stine Hansen knows?

With respect.

(CID:137110431)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

Hi Folks,

The Resources menu and "feature requests" can also be used in case of a bug. I looked at this but have not yet tested it so I've not entered anything in the system.

 

Steve

(CID:137110441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

Thanks Steve. I'll try to submit a request there and hopefully get a resolution.

Brian

(CID:137110462)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

Hello,  Brian and I have spoken over email.  I did some testing and believe that this is a bug.  Seems as though the auth and priv passphrases are not being set over CLI, all other settings appear to work.  This is logged in our bug tracking tool and should hopefully be fixed soon.  If anyone has any questions please let me know.

Thanks.

(CID:137111337)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

0 Likes
1
2620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

This issue appears to have been resolved by firmware update 6.6.7.

(CID:137725881)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

In response to DCIM_Support
0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2024-04-03 11:34 PM

Ok, very thanks for the feedback.

(CID:137725928)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2023-10-22 03:16 AM

0 Likes
0
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 03:11 PM . Last Modified: ‎2023-10-22 03:16 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore