NetBotz failing HTTP post to StruxureWare DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz failing HTTP post to StruxureWare DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

0 Likes
4
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

NetBotz failing HTTP post to StruxureWare DCE

StruxureWare DCE not capturing sensor and surveillance data from NetBotz 750. NetBotz event log has the following errors.

daemon.err nbSendHTTPReport: Error posting to url http://DCE:80/botpost/sensor: HTTP code=0, err=7
daemon.err nbSendHTTPReport: All URLs failed
daemon.err nbSurveilMgr: Error posting to url http://DCE:80/botpost/surveillance: HTTP code=0, err=7
daemon.err nbSendHTTPReport: All URLs failed

(CID:147196909)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

0 Likes
2
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

Hi Barry,

Surveillance is not yet supported between DCE and the NetBotz 750. This will require not only DCE 7.7 which is currently release but also BotzWare 5.2 which is due out (tentatively) next month or so. 

This is noted here:

https://sxwhelpcenter.ecostruxureit.com/display/SWDCDOC/PDF+Library?preview=/96044657/145425629/Stru...

 

It's also mentioned here:
http://www.apc.com/us/en/faqs/FA375552


Thanks,

Steve

(CID:147197194)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

In response to DCIM_Support
0 Likes
0
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

Hello Steve, it appears the NetBotz is a 570 that's having an issue sending data to the DCE appliance.

(CID:147197522)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

In response to DCIM_Support
0 Likes
0
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2024-04-03 01:03 AM

Hi Barry,

The first thing I would look at is the the data center expert applet in Advanced View. How many DCE servers are listed (if using surveillance, should be 3 posts per server). If you're posting to too many, perhaps you should limit the amount of servers to one or two. Also looking at this applet, if the bot is posting to hostname, you may want to consider changing it to IP. TO do so you'd need to delete these entries then go to DCE to set the post up correctly.

In DCE, go to the device menu, NetBotz Appliance Configuration–>Post Alert Data Settings. Select the address to use for sending alert data and choose the IP rather than hostname and hit OK. If you're using surveillance, you'll also want to go into the device menu and Surveillance Settings. Select the camera(s) for this bot and where it shows server settings/StruxureWare Data Center Expert Server, enter that server's IP and apply. These 2 settings should now be set on the NetBotz appliance.

If there is some sort of firewall between the appliance and DCE, you can also put the NetBotz appliance into post only mode. The following k-base outlines how to configure post only mode:

http://www.apc.com/us/en/faqs/FA158263

 

If the issue is intermittent, that's harder. These messages may occur randomly and simply be an issue with network traffic. To test this, you may want to change the subnet of this appliance to a segment that may work with another appliance or put it on the same segment as the DCE server. 

 

You may also want to try discovering via https instead of http in case http is being blocked by your network / firewall. 

 

Steve

 

(CID:147197526)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2023-10-22 03:15 AM

0 Likes
0
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 08:52 PM . Last Modified: ‎2023-10-22 03:15 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore