NetBotz 570 Data Log period?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 570 Data Log period?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

0 Likes
5
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

NetBotz 570 Data Log period?

Hi,

Please i need to know for how long does the NetBotz 570 log data.

From Advanced View 4.5.4, i can view and extract logged data for only 8 hours.

(CID:122689751)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

0 Likes
1
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

Hi Momen Samy,

As correctly stated in reply Steven Marchetti in the post , by default, the NetBotz will only store up to 24 hours of data. See, for example, this screenshot:

But, as stated in the post Netbotz 500 challenges on APC forum:

6. You can designate any NFS or Windows CIFS/SMB share as external storage for the NetBotz 500. This is done in the Advanced View, under the section for External Storage (in your Configuration perspective). It will ask you to specify the type of share you are going to use, and then to provide the IP/hostname, credentials, and share name of the specified network location. Although the data will be stored externally to the NetBotz appliance, you are still only able to access historical alerts or graphs via the NetBotz Advanced View. You can view past information in the Alerts View or the Graph View. You'll notice that once you configure external storage, the time frame that is available for viewing will increase from multiple hours to multiple days or months.

With respect.

(CID:122689767)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

0 Likes
1
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

Hi Momen Samy,

As correctly stated in reply Steven Marchetti in the post , by default, the NetBotz will only store up to 24 hours of data. See, for example, this screenshot:

But, as stated in the post Netbotz 500 challenges on APC forum:

6. You can designate any NFS or Windows CIFS/SMB share as external storage for the NetBotz 500. This is done in the Advanced View, under the section for External Storage (in your Configuration perspective). It will ask you to specify the type of share you are going to use, and then to provide the IP/hostname, credentials, and share name of the specified network location. Although the data will be stored externally to the NetBotz appliance, you are still only able to access historical alerts or graphs via the NetBotz Advanced View. You can view past information in the Alerts View or the Graph View. You'll notice that once you configure external storage, the time frame that is available for viewing will increase from multiple hours to multiple days or months.

With respect.

(CID:122689767)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

In response to DCIM_Support
0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

Thanks sir for the clear answer..

(CID:122689789)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

0 Likes
1
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

Hi Momen,

 

If you look at the individual sensors, you'll see that 8 hours is the default. The maximum setting is 1 day as seen here:

To get more data storage, the preferred method would be to use this in conjunction with StruxureWare Data Center Expert (DCE) where you will be limited only by the size of the drives on the system or external repositories should you be using one.

You can use a USB drive on a 570 directly as well as using a network share when configuring the "External Storage" optuion. Should the appliance reboot however, some data may be erased whereas using DCE that will not happen.

 

Thanks,

Steve

(CID:122689770)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

In response to DCIM_Support
0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2024-04-08 12:03 AM

Thanks for clarification

(CID:122689790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2023-10-22 03:12 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:51 PM . Last Modified: ‎2023-10-22 03:12 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore