NetBotz 450 Communication Error with DCE 7.3.1

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 450 Communication Error with DCE 7.3.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

0 Likes
8
1577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

NetBotz 450 Communication Error with DCE 7.3.1

Hi,

We have 4 x NetBotz 450 Monitors.  The network connection to all of them goes online and offline constantly, generating "Communication Error" alerts for the Netbotz Rack Monitors and the Sensor Pod.

I can ping the IP addresses to all 4 of the NetBotz monitors successfully, before, during and after DCE reports them as having a Communication Error.

(CID:108825718)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Hi Michael, The NetBotz need a baud rate of 38400. If you can't log on to them using http or https, it is likely that DCE can not log on to them either. I'd suggest getting the serial configuration working then using a crossover cable, verify the web is working. Perhaps a configreset of the device is required. http://www.apc.com/us/en/faqs/index?page=content&id=FA158175 or a reflash of the firmware http://www.apc.com/us/en/faqs/index?page=content&id=FA176133 If you reflash, don't use the keep option if you want to reset the device totally. Steve

(CID:108825802)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

0 Likes
3
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Hi Michael,

 

Ping uses a different port and protocol than the NetBotz to DCE communications. Ping can be helpful if a node is down or network is dropped but you'd want to run the ping from the Device to server or server to device rather than from say your laptop to either. 

When they're off-line, I suggest trying to access the web interface of the DCE server and the web interface of the NetBotz appliance. I suggest using the same protocol with which the appliances were discovered. If they're communicating HTTPS, connect using HTTPS. If http, use http. 

 

I'd also be curious to know if they're all going off-line around the same time.

How often is it happening and how long does it last?

What are the polling settings for these botz. What version of Botzware is being run on the appliances?

Are the  appliances on the same network segment as the other 3? Are they on the same segment as DCE?

Are you monitoring other NetBotz devices other than these 4 and if so, do they have issues?

Are you monitoring SNMP/modbus devices as well?

Are you using surveillance?

 

Steve

(CID:108825720)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

In response to DCIM_Support
0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Hi Steve,

 

I use ping from a different subnet to see if there a network / switch / port issue communicating to these devices.  The pings do not fail, from my workstation.

 

I'd also be curious to know if they're all going off-line around the same time.

  -  Yes, they are all going offline and online at the same time

How often is it happening and how long does it last?

  -  It varies, but they go offline for about 30 minutes, come online for a while and then continue the cycle going offline, online, etc

What are the polling settings for these botz. What version of Botzware is being run on the appliances?

  -  Not sure, but I think they are set to 5 mins (from the default of 10 mins).  The version is V4_5_2_20160602_1247

Are the  appliances on the same network segment as the other 3? Are they on the same segment as DCE?

  - All 4 of the appliances are in the same room, and are on the same network.  The DCE is on a different subnet

Are you monitoring other NetBotz devices other than these 4 and if so, do they have issues?

  - No other NetBotz devices are being monitored at this time, but we are installing and configuring DCE, so some other rooms will come online when we can

Are you monitoring SNMP/modbus devices as well?

  - I have 2 x RDU cooling units with 14 CMs, and 56 AP8868 PDU's being monitored, all in the same room, and all on the same subnet as the Netbotz appliances

Are you using surveillance?

  - No

(CID:108825804)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

In response to DCIM_Support
0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Hi Steve,

I've just discovered that I can't actually sign into the NetBotz appliances over the network using either IE or Firefox.  I also tried the serial connection to 1 of the appliances, but that didn't respond using 8-none-1, 9600

 

(CID:108825805)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

In response to DCIM_Support
0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Hi Michael, I understood that the pings didn't fail from the workstation, I was just curious if you could get to the web interface of DCE or the device, you could, from that interface, ping the other device. On DCE the ping option is: http:// of the DCE server>/nbc/status/Troubleshoot and from the bot, you can ping using: http:// of bot>/pages/support.html You may want to work with local tech support to look a the logs of the DCE server. If all devices are going off-line around the same time and it's lasting for 30 minutes, it doesn't sound like it's the individual appliances. It sounds like it's either network related or DCE related. If you could move one of the appliances local to the DCE server, that may also indicate something. If it's in the local LAN and it has the same issue, that would point toward DCE and if the local bot does not see the same comm issue, it's a pretty good indication that it's network. Steve

(CID:108825806)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

0 Likes
0
1577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Hi Michael, The NetBotz need a baud rate of 38400. If you can't log on to them using http or https, it is likely that DCE can not log on to them either. I'd suggest getting the serial configuration working then using a crossover cable, verify the web is working. Perhaps a configreset of the device is required. http://www.apc.com/us/en/faqs/index?page=content&id=FA158175 or a reflash of the firmware http://www.apc.com/us/en/faqs/index?page=content&id=FA176133 If you reflash, don't use the keep option if you want to reset the device totally. Steve

(CID:108825802)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

0 Likes
1
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:11 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Hi Steve,

The configreset did the trick.  After I reset all of the Netbotz devices, the network connectivity problems have disappeared (for over 4 days now πŸ˜€).  I suspect that after we upgraded the firmware via DCE, the devices needed to be reset, but there was no indication that this was required.

 

Thanks again for all of your help!

(from a DCE rookie...)

(CID:108826111)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:12 AM . Last Modified: β€Ž2024-04-08 10:53 PM

In response to DCIM_Support
0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:12 AM . Last Modified: β€Ž2024-04-08 10:53 PM

Thanks for the update Michael. That shouldn't have happened but since it did to multiple units, it sounds like something corrupt (possibly a setting) got pushed to all the units. If resetting did the trick, it doesn't sound like bad FW. Steve

(CID:108826259)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 06:12 AM . Last Modified: β€Ž2023-10-31 11:24 PM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 06:12 AM . Last Modified: β€Ž2023-10-31 11:24 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore