NetBotz 150 attached to 200 Sensor Errors

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NetBotz 150 attached to 200 Sensor Errors
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2024-04-08 11:41 PM

0 Likes
3
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2024-04-08 11:41 PM

NetBotz 150 attached to 200 Sensor Errors

Hello All

 

We have a Customer who has the Following installation:

 

Netbotz 200 and connected to this extensions with Sensor Pods 150

On the Sensor Pods 150 he has connected some T and TH Sensors.

These Sensors sometimes return zero values like at the below Diagram

 

Has someone any idea what could cause this issue

We told the Customer to check the following Points:

1st
Could you please check if there is a Power Supply connected at the NetBotz Sensor Pod 150 where you have such issues? If not there is may be the Problem of Voltage to low because of to many sensors connected to the same Bus. (NetBotz 200 --> Sensor Pod 150)

2end
Could you please send me the Serial numbers of the NetBotz 200 which you have installed? You can export them from the Data Center Expert Server using Inventory Report. We had earlier a Model where we where Facing such issues because of a problem with the Power Supply at the NetBotz 200 according our Engineering. If you send me the Serial numbers I can ask them to check this.

3rd
Could you please tell me which Firmware Version currently is installed on the NetBotz 200? This is also possible to check at the Data Center Expert Server in Monitoring View there is a column named Application Version. Newest Version is 3.7.6 and is available for Download here:
http://www.apc.com/shop/ch/de/products/NetBotz-Rack-Monitor-200-mit-120-240V-Energieversorgung-/P-NB...

4th
Could you please send us the Version of Data Center Expert you are using. If you click on Help at the Client you will find About SturxureWare Data Center Expert. Or at the header of the Client there is the Version mentioned as well after StruxureWare Data Center Expert.

 

Is it Possible to suppress the zero vaules on DCE somehow?

 

Best Regards

Patrick

(CID:106210287)

Labels
  • Labels:
  • Data Center Expert
  • DDF
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2024-04-08 11:41 PM

0 Likes
1
819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2024-04-08 11:41 PM

Hi Patrick,

 

It is not possible to suppress values. You can export the data and have a tool like Excel find and delete 0 values for you and graph it there but it's not an option in DCE, sorry.

 

I would suggest looking to see what it's coming from. You've got some good steps above but I would suggest looking at a little more. Take a look at the data log on the device. Is the device itself reporting these 0 values? If so, we know it's a device issue. Another way to look for this would be to set up an SNMP poll of the sensors doing it most often. Does an independent scan of the sensor record 0 values as well? Are they all the same type of sensor? What sensor are they? If both temp and humidity, does the humidity do the same thing?

 

Is this all coming from the same device or multiple devices? Are all the sensors reporting this 0 value (there do seem to be a few) connected to the same sensor pod? If you swap around sensors that are doing this with sensors that are not, does the issue follow the port or sensor? Are any of the sensors using extension cables? What are the distances for the sensors and pods?

 

Steve

 

 

(CID:106210311)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2024-04-08 11:41 PM

In response to DCIM_Support
0 Likes
0
819
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2024-04-08 11:41 PM

Hello Steven

Thanks very much for your Feedback according this.

Some of your additional Question we discussed with the customer already earlier like:

This Error is not a Server related problem because the Error Values are coming from the Netbotz

Alert Title: Temperature - DTC2_D12_4_TH - value rising too quickly - 20.0 ° C
Alert Description: The value of 'Temperature - DTC2_D12_4_TH' (20.0 ° C) is rising too quickly.
Alert Type: Value Rising Too Quickly
Severity: Error
Alert Level: EXPERT Threshold alert
Sensor: Temperature - DTC2_D12_4_TH
Sensor Value: 20.0 ° C
Device: DTC2APC01(10.136.98.201)
Time Detected: 07/22/16 00:54:31
Notification Time: 07/22/16 00:54:31
Notification Policy: GHE mail
Action Name: EXPERT Threshold alert
Location: DTC2_N09
Primary Contact: GLO-GIS-L3-Physical site mgt
Notes: APC Web/SNMP Management Card (MB:v4.0.6 PF:v3.7.5 PN:apc_hw03_aos_375.bin AF1:v3.7.5 AN1:apc_hw03_nb200_375.bin MN:NBRK0200 HR:05 SN: ZA1509001936 MD:02/24/2015)
Alert ID: nbErrorCond_1B0C5095
Version: 7.2.7.25

 

 

The Customer has switched over all his components and unfortunately the Error is not Consistent. There is not a Port where we can locate the error or a failing sensor.

The extensions are all in about 10 Meters Range

There are T and TH Sensors connected and both of them sometimes Fail. 

 

Answers to my Questions above from Customer site:


1st yes our both POD 150 are powered by a power supply

2nd ZA1509001961 & ZA1509001936

3rd V3.7.5 (the web site you mentioned show only v3.7.5 and v3.5.6, so the 3.7.5 seems to be the last)

4th Client Build: 7.2.7.25 / Server Build: 7.2.7.25 / Serial Number: WV1505TGKK41

 

 

Do you suggest to try different Hardware?

 

Patrick

 

 

 

 

(CID:108825462)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2023-10-31 11:23 PM

0 Likes
0
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:21 AM . Last Modified: ‎2023-10-31 11:23 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of