Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

NetBOTZ 750 Giving Failed to authenticate with the device API. IN DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBOTZ 750 Giving Failed to authenticate with the device API. IN DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
shoaibmaqsood52
Lieutenant JG shoaibmaqsood52
Lieutenant JG

Posted: ‎2023-03-29 11:54 PM

1 Like
4
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-29 11:54 PM

NetBOTZ 750 Giving Failed to authenticate with the device API. IN DCE

Hello,

 

I have discovered the 9 Netbotz 750  in DCE with the same firmware (5.2.1). Only one Netbotz 750 is giving the below error in DCE. 

Failed to authenticate with the device API. As a result, the device may fail to show any connected cameras.

 

 

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2023-04-03 06:10 AM . Last Modified: ‎2023-04-03 06:13 AM

1 Like
0
2894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-03 06:10 AM . Last Modified: ‎2023-04-03 06:13 AM

Hi @shoaibmaqsood52 ,
As you look through the following FAQ:
https://www.apc.com/us/en/faqs/FA381605/

Follow the info on how to transfer certs between the DCE and NetBotz or how to use no verification.

 

Additionally, I have noticed that in DCE if you have too many wild cards when it comes to this part:

Device menu --> NetBotz Appliance Communication Settings --> NetBotz Appliance Credentials

It may not work. I recommend adding an individual entry with the specific IP of the unit you're having an issue with.

Additionally, if you have added a secondary user and are using that user instead of superuser for the "NetBotz Appliance Credentials" in DCE, please make sure that this user has logged into the NetBotz appliance directly at least once.

 

Thanks,

Steve

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2024-05-14 05:48 AM

0 Likes
1
2067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-14 05:48 AM

Hi,

 I've same error message with a NB750 WITHOUT any camera connect

=> how to remove this error message

Reply

Link copied. Please paste this link to share this article on your social media post.

Gabi
Lieutenant Gabi
Lieutenant

Posted: ‎2024-05-20 03:54 AM

In response to Dominique38
0 Likes
0
2032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-20 03:54 AM

Hello,

 

use FAQ link from @APC_Steve ....your DCE is set to verify netbotz certificate(by default is self signed and cannot be verified)

Reply

Link copied. Please paste this link to share this article on your social media post.

Dominique38
Ensign Dominique38 Ensign
Ensign

Posted: ‎2024-05-22 07:37 AM

1 Like
0
2015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-22 07:37 AM

Hi, after applying /netbotz_app/factory_reset.sh in SSH console mode, NB and DCE are working fine.

Before, there was the error Failed to authenticate with the device API..... and unable to discover a camera

After factory reset, NB discover camera and error disappear.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore