NBRK0450 + AP9335TH: no measured humidity values below 14% RH?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NBRK0450 + AP9335TH: no measured humidity values below 14% RH?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:37 AM . Last Modified: ‎2024-04-05 03:15 AM

0 Likes
3
572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:37 AM . Last Modified: ‎2024-04-05 03:15 AM

NBRK0450 + AP9335TH: no measured humidity values below 14% RH?

Hi all!

To me it is important to the opinion of experts who are here: what is the minimum allowable humidity can be measured by a combined sensor AP9335TH, which is connected to the NetBotz-450?

I now observe a situation, when the room humidity became below 14% RH. At the same time, the historical report in APC Advanved View on the humidity sensor shows the absence of measured humidity values in general. This is also displayed on the graphical reports of the DCE-server, for example:

Can someone confirm my observations and assumptions?

Very thanks for the support.

(CID:128062237)

Labels
  • Labels:
  • NetBotz
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:37 AM . Last Modified: ‎2024-04-05 03:15 AM

0 Likes
0
572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:37 AM . Last Modified: ‎2024-04-05 03:15 AM

Hi all!

I supplement my question with one more observation: if the combined sensor AP9335TH is connected to the NMC2 AP9635CH (for example, in the Symmetra PX250/500 UPS), it is possible to measure humidity even below 14% RH. All this is clearly visible on my screenshot:

Therefore, I concluded that the above problem is related specifically to the combination of the connection AP9335TH + NetBotz-450.

Very thanks for the support.

(CID:128062656)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:37 AM . Last Modified: ‎2024-04-05 03:15 AM

0 Likes
0
572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:37 AM . Last Modified: ‎2024-04-05 03:15 AM

Hi all!

Today, I was able to determine the minimum possible humidity, which can be measured with the AP9335TH sensor connected to rPDU AP8853 - this is 10% RH:

I understand, that it is already impossible to measure the lower humidity because of the measurement error. But even in such a combination, i.e. AP9335TH + AP8853 with minimal humidity there are no gaps on the humidity chart as it is observed in the case of AP9335TH + NetBotz-450.

With respect.

(CID:128066511)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:38 AM . Last Modified: ‎2023-10-22 03:08 AM

0 Likes
0
572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:38 AM . Last Modified: ‎2023-10-22 03:08 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of