Posted: 2020-07-05 09:58 PM . Last Modified: 2024-04-03 12:37 AM
Hi Team ,
We have netbotz 750 which have 4 pod165 camera on customer site , we found two of four are very
blurry , we can adjust focal length by pod160 but not sure if pod165 also can do that ?
Posted the blurry and clear one for your reference .
And some camera can not entry the setting page , it's show "failed to get camera configurations for cameraXX (404)" when click the setting button . Can someone advice? Your input would be appreciated .
Best Regards



(CID:148344671)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:59 PM . Last Modified: 2024-04-03 12:37 AM
Hi,
Sorry for any delay in responses.
The manual is here:
You mentioned:
we can adjust focal length by pod160 but not sure if pod165 also can do that ?
The manual has the following for focus:

Thanks,
Steve
(CID:148769985)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:58 PM . Last Modified: 2024-04-03 12:37 AM
Hello ,
Can someone expert know this issue?
(CID:148769841)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:59 PM . Last Modified: 2024-04-03 12:37 AM
Hi,
Sorry for any delay in responses.
The manual is here:
You mentioned:
we can adjust focal length by pod160 but not sure if pod165 also can do that ?
The manual has the following for focus:

Thanks,
Steve
(CID:148769985)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:59 PM . Last Modified: 2024-04-03 12:37 AM
Thank you Steve , will try out few days later .
(CID:149291076)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:59 PM . Last Modified: 2024-04-03 12:37 AM
Dear Chu Li Wei,
Please tell us, were you able to solve your problem or not?
With respect.
(CID:148771886)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 09:59 PM . Last Modified: 2023-10-22 03:07 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.