Dear Team,
I am aware a single NBPD0150 can only support two of NBES0303 sensor, how many NBES0302 sensors can be supported by a single NBPD0150?
Thank you.
Regards,
Felix.
(CID:124522127)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:25 PM . Last Modified: 2024-04-07 11:05 PM
Hi Felix,
In both cases, the netbotz 150 pod can support up to 6 nbes0302 or 0303 sensors. Have you seen documentation stating otherwise?
steve.
(CID:124522133)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:25 PM . Last Modified: 2024-04-07 11:05 PM
Hi Felix,
In both cases, the netbotz 150 pod can support up to 6 nbes0302 or 0303 sensors. Have you seen documentation stating otherwise?
steve.
(CID:124522133)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:25 PM . Last Modified: 2023-10-22 03:07 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.