Can someone point me to an article that describes what I think is a common configuration for DCO?
I have a 30A Rack Power Distribution (CDU). It uses 2 20A breakers from the PDU to provide 30A. How do I represent the two circuits from the one PDU breaker panel to the single power strip in the rack?
Thank you in advance.
(CID:129413675)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:01 PM . Last Modified: 2024-04-05 12:21 AM
short answer, you can't model a single rack pdu with 2 single source power feeds. Every breaker can only have a 1:1 relationship with the rack pdu. The only exception to this would be for an ATS, but that's for redundancy.
This would instead have to be modeled as 2 separate rack pdus each with half of the outlets. I assume each 20a circuit powers a separate outlet bank on the rack pdu??
I don't foresee this ever changing since it really isn't a current data center best practice to do this and was something that was typically only seen in legacy data centers before 3ph rack pdus were more prevalent.
If i misunderstood your question or you have a good use case for why this should be available in DCO (other than it exists), please feel free to elaborate. You can also make a feature request for it.
(CID:129413681)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:01 PM . Last Modified: 2024-04-05 12:21 AM
short answer, you can't model a single rack pdu with 2 single source power feeds. Every breaker can only have a 1:1 relationship with the rack pdu. The only exception to this would be for an ATS, but that's for redundancy.
This would instead have to be modeled as 2 separate rack pdus each with half of the outlets. I assume each 20a circuit powers a separate outlet bank on the rack pdu??
I don't foresee this ever changing since it really isn't a current data center best practice to do this and was something that was typically only seen in legacy data centers before 3ph rack pdus were more prevalent.
If i misunderstood your question or you have a good use case for why this should be available in DCO (other than it exists), please feel free to elaborate. You can also make a feature request for it.
(CID:129413681)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:01 PM . Last Modified: 2023-10-22 03:04 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.