Posted: 2020-07-04 04:01 PM
This question was originally posted on DCIM Support by Brady Burke on 2018-03-30
Can someone point me to an article that describes what I think is a common configuration for DCO?
I have a 30A Rack Power Distribution (CDU). It uses 2 20A breakers from the PDU to provide 30A. How do I represent the two circuits from the one PDU breaker panel to the single power strip in the rack?
Thank you in advance.
(CID:129413675)
Posted: 2020-07-04 04:01 PM
This answer was originally posted on DCIM Support by Andrew Trabert on 2018-03-30
short answer, you can't model a single rack pdu with 2 single source power feeds. Every breaker can only have a 1:1 relationship with the rack pdu. The only exception to this would be for an ATS, but that's for redundancy.
This would instead have to be modeled as 2 separate rack pdus each with half of the outlets. I assume each 20a circuit powers a separate outlet bank on the rack pdu??
I don't foresee this ever changing since it really isn't a current data center best practice to do this and was something that was typically only seen in legacy data centers before 3ph rack pdus were more prevalent.
If i misunderstood your question or you have a good use case for why this should be available in DCO (other than it exists), please feel free to elaborate. You can also make a feature request for it.
(CID:129413681)
Posted: 2020-07-04 04:01 PM
This answer was originally posted on DCIM Support by Andrew Trabert on 2018-03-30
short answer, you can't model a single rack pdu with 2 single source power feeds. Every breaker can only have a 1:1 relationship with the rack pdu. The only exception to this would be for an ATS, but that's for redundancy.
This would instead have to be modeled as 2 separate rack pdus each with half of the outlets. I assume each 20a circuit powers a separate outlet bank on the rack pdu??
I don't foresee this ever changing since it really isn't a current data center best practice to do this and was something that was typically only seen in legacy data centers before 3ph rack pdus were more prevalent.
If i misunderstood your question or you have a good use case for why this should be available in DCO (other than it exists), please feel free to elaborate. You can also make a feature request for it.
(CID:129413681)