Managing MODBUS Device through Netbotz
  • Managing MODBUS Device through Netbotz
129
72
Posted: ‎2020-07-02 03:55 PM . Last Modified: ‎2024-04-09 02:59 AM
665
Is there a supported list of gateway that supports the conversion of MODBUS TCP / RTU to SNMP via Netbotz - NBWN0006 (Netbotz Device Monitoring 5 Nodes Pack)
(CID:103583886)
  • NetBotz
Posted: ‎2020-07-02 03:56 PM . Last Modified: ‎2024-04-09 02:59 AM
Hi Bernard,
Are you looking to monitor a Modbus device using a NetBotz appliance? I would not recommend this. I would suggest monitoring the modbus device with DCE, perhaps the free VM. If you do find a gateway (we don't support any for this purpose) so that the NetBotz appliance can monitor your Modbus device now SNMP, we are not currently creating DDF files for the NetBotz appliance so you'd need to manually add all OIDs using the supplemental OID feature in the SNMP scanner applet. Additionally, you won't be able to read text and there are no multipliers so a voltage of 120 volts in tenths will potentially appear as 1200.
Steve
(CID:103583888)
Posted: ‎2020-07-02 03:56 PM . Last Modified: ‎2023-10-31 11:21 PM