We had 83 out of 84 devices in a group set to be in Maintenance Mode for the past few days. This morning, we got alerts on a bunch of these devices. I double-checked and they still show up as being in Maintenance Mode in the DCE console... what went wrong here?
(CID:151062615)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 11:15 PM . Last Modified: β2024-04-03 12:11 AM
Check the web interface of the devices for email configuration. If email notifications are configured on the device itself, they will still send emails. Maintenance mode only disables notifications sent by DCE.
(CID:151062868)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 11:15 PM . Last Modified: β2024-04-03 12:11 AM
Try to check`s recipents of all decivices in each interface web. Becauses maybe the problem is there. And try to do a test When you active any parameters in the DCE.
(CID:151062971)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 11:15 PM . Last Modified: β2023-10-22 03:00 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.