I am trying to use a TM221CE40R to communicate through the serial port using Modbus RTU. I have a Waveshare USB to RS485 device going to my computer. I set up the Write_Var to multiple words and it works fine. I try to set up the Write_Var to bits and monitor the addressed coils and I get nothing. Figure I don't understand what all the fields mean - thinking the index is not correct. My guess was 40 means %M40.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-15 05:42 AM
Found a solution last night. A YouTube video in Portuguese. ( I know some French and a tad of Spanish). The index was my issue. an index of 40 would refer to %MW40 then look for %MW40:x0 for the coil.