MODBUS Comm Link Issue with Multiple Slaves

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • MODBUS Comm Link Issue with Multiple Slaves
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:36 AM . Last Modified: ‎2024-04-09 12:33 AM

0 Likes
4
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:36 AM . Last Modified: ‎2024-04-09 12:33 AM

MODBUS Comm Link Issue with Multiple Slaves

We have 4 slave generators which communicate with DCE via an internet gateway device (ComAp's IB-NT). The comm. link for the slave devices went up and down. It appears that only one slave is up at a time. What could be the problem and what is the solution. Can DCE works with multiple slaves via gateway device?

 

I tried to change the timeout to different values and see no difference.

(CID:105470162)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:36 AM . Last Modified: ‎2024-04-09 12:32 AM

0 Likes
2
830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:36 AM . Last Modified: ‎2024-04-09 12:32 AM

Hi Yang,

 

DCE is definitely capable of communicating with multiple slave devices on a single gateway. The only gateway we have tested and support at this point is the modbus wired to modbus over IP gateway TSXETG100 but similar devices should work.  Have you tried polling the different devices manually from the same subnet as DCE?

 

You may also want to look at the baud rates used on the wired side of the gateway. I believe higher baud rate on the devices and gateway may allow for a faster transfer of data and potentially less comm issues. You can test faster / slower rates.

 

If you have any other systems communicating to these devices, that could also cause comms issues. If you have such a configuration, stop the other system (serial or over IP) from monitoring the devices for at least a test period. 

 

You may also be able to run a packet capture to see if the devices are responding or if DCE is even polling. SOme gateways also have troubleshooting utilities that can log this type of data but you'd need to check their manual or support options for that info.

 

Steve

(CID:105470172)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:36 AM . Last Modified: ‎2024-04-09 12:32 AM

In response to DCIM_Support
0 Likes
0
831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:36 AM . Last Modified: ‎2024-04-09 12:32 AM

DCE has no problem to talk to a single MODBUS device (without gateway). DCE may have problem to talk to multiple slave device with common gateway. Here is my understanding about the problem. When DCE send a polling request to a device, it requires to establish TCP/IP communication with the remote device. Once a reply is received, it clear the TCP/IP communication with remote device. During TCP/IP session, another polling request from different server to the same remote device will be rejected. In the case of multiple slave devices on the same gateway, if DCE sends polling requests for all slave devices in a relative close time interval, some requests will be rejected if the previous TCP/IP session has not been cleared. The problem is user can not control the polling interval among the devices. I tried with 2 slave devices with polling interval between the 2 devices about 30 to 60 seconds and the global scanning at 2 minute, I had no comm. link issue. is there any way DCE can set or control the polling interval among the slave devices with common gateway.?

(CID:105470194)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:37 AM . Last Modified: ‎2024-04-09 12:32 AM

In response to DCIM_Support
0 Likes
0
832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:37 AM . Last Modified: ‎2024-04-09 12:32 AM

Hi Yang, That may be the case and again that's why I suggested looking at the gateway. There is no way to set polling delays between different devices. If the gateway you're using is having issues when polling another device within a few seconds of the first, then perhaps another type of gateway or multiple gateways are required. Again, issues like that can in some cases be effected by changing baud rates. Since DCE is meant to be capable of monitoring up to 4025 devices, making it possible to create delays of 20 or 30 seconds between polls would be impractical and would itself cause issues. There would also be quite a bit more code required to make such delays possible between different devices on the same IP/gateway. Steve

(CID:105470196)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:37 AM . Last Modified: ‎2023-10-31 11:22 PM

0 Likes
0
832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:37 AM . Last Modified: ‎2023-10-31 11:22 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore