Ask our Experts
Didn't find what you are looking for? Ask our experts!
Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-20 05:53 AM
Hello all,
I have been updating our Netbotz rack monitors and so far when I come from 5.2.1 to 5.4.1.5027 (via 5.3x) I have lost access to the GUI both times.
I've run the commands to clear the database, restart clubber, and even factory reset but I can't seem to restore the web GUI. The only access I have is SSH.
I noticed that prior to the update there were three files in the landing folder (/home/root😞 config.ini, config.ini.backup and ddf.zip. Post update there is only ddf.zip and nohup.out.
config.ini contains the general settings including network and SNMP details. Is it helpful to edit that file from a working monitor and replace it there?
Or is there a better way to restore the GUI?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-02 03:12 AM
EMEA Tech Support helped me resolve this.
Clearing the database and factory reset didn't help.
The solution was to revert to the last working firmware:
run flip_banks
boot
In one case that was an end of it.
In the other I was left with 503 errors on the web GUI but that was resolved by clearing the database.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-21 03:31 AM
Also, I wondered - without the web GUI - is there anyway to roll back the last upgrade?
Something like active partition options where the previous version is in the other partition.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-22 09:44 AM
Hello @Hogg
You'll get the best and fastest results if you contact support for help with this issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-23 01:23 AM
Thanks.
I'm waiting on a response there already.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-09 02:22 AM
Hello @JLehr,
How long is it usually before a support ticket gets a response?
I gave it a nudge comment after a week or so but still nothing and that was a week ago.
Is calling them possible/better?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-10 05:57 AM . Last Modified: 2025-07-03 06:14 AM
Hi @Hogg,
Yes, please contact your local support again. It will help to have your support ticket number available.
It's unusual that you'd be waiting so long. Apologies for that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-10 06:08 AM
Thanks. Will do.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-02 03:12 AM
EMEA Tech Support helped me resolve this.
Clearing the database and factory reset didn't help.
The solution was to revert to the last working firmware:
run flip_banks
boot
In one case that was an end of it.
In the other I was left with 503 errors on the web GUI but that was resolved by clearing the database.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.