Lost Communications Error

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Lost Communications Error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

0 Likes
11
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

Lost Communications Error

Is anyone experiencing DCE VM (colo) edition intermittently losing communications with sensors and/or meters?  The error "lost communications" with some PDUs appears every couple of nights around 1am.  The DCE instance is running on a VMware platform which is connected to a separate VLAN than the sensors/meters. Does DCE need to be on the same VLAN to stop this happening - or are there any other suggestions?

(CID:93192917)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

I had the same issue, here are the steps which I took to resolve it.

All devices have the IP Addresses set statically

I removed all the devices from DNS and added them manually with static IP addresses.

Also I have excluded the IP addresses from DHCP (the devices have them set manually but think that DHCP was trying to issue them hence loosing connection).

From my understanding, DCE doesn't have to be on the same VLAN, as long as the VLAN it is on can ping the Netbotz and sensor pods.

 Hope this helps.

(CID:93192941)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

Hi Mike,

 

Without having network packet captures during the time of the lost comms, it's tough to know exactly what the reason would be. If this seems to be a specific subset of PDUs (and they're SNMP), you can try to up the timeout or retries on these devices and see if that addresses the problem. I would start with timeout since we already have 3 retries by default.

 

The setting is under the Device -> SNMP Device Communication Settings -> Device Scan Settings.

If they're Modbus PDUs, there is also a timeout setting available under the "Device" menu.

 

The fact that they're on a separate VLAN should not be a problem, especially since you've already discovered them and are getting sensor data 99% of the time.  If you were not able to discover them initially then I'd say you'd need to look more closely at the network configuration. 

 

(CID:93192965)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

0 Likes
4
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

Thanks Martin & Scott - we'll look into both suggestions. Appreciate the responses.

(CID:93193044)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

In response to DCIM_Support
0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

Hi Mike, Did you manage to get the issue resolved?

(CID:93193242)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

In response to DCIM_Support
0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

We upped the retry time from 5 secs to 30 secs - but it does not appear to have had any affect. We'll look to increase the number of retries next.

(CID:93193262)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

In response to DCIM_Support
0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

Adding onto this - we're now aware of three separate customer deployments all experiencing the same "Lost Communications" error. By the way - the issue is evident both with APC PDUs and SNMP comms to bus-duct meters with custom DDFs. Our tech team had previously updated the number of retries to 5 which didn't fix it. Not sure if we've done number of retries and timeout at the same time - but we plan to.

(CID:93193263)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

In response to DCIM_Support
0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:21 AM . Last Modified: ‎2024-04-10 01:15 AM

Has anyone made any progress on this problem?  We have several hundred monitored devices (Rack PDUs (both APC and other vendors), APC RDUs, NetBotz 450, and some environmental monitors by IMCI).  We frequently get "Communication Lost" alerts from random devices.

I did try and modify the retries and timeouts, but this didn't appear to bypass the problem.  I've also done continuous pings to the devices, and the devices respond to the pings 100% of the time.

 

Thanks

(CID:118000823)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2024-04-10 01:15 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2024-04-10 01:15 AM

You can add me to the list of customers experiencing Coms Loss.  It happens for (usually) one poll and then recovers on the next.  Setting the timeout or poll rate differently does not affect the problem (only effects how often you see if it you slow the poll down).   We have had Schneider look at it but they only fiddle with the poll interval and time out which does not solve the problem.

The cause is that DCE alarms on the first occurrence of Coms Loss and while we don't know what the cause is we do know it will happen.

What we have asked is for a "State for Time" setting be added to the Communication Status threshold as an enhancement.  But in the mean time you may need to get creative.

My 2 cents.

(CID:96043083)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2024-04-10 01:15 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2024-04-10 01:15 AM

Out of interest, does the DCE server perform automatic backups?  We have suspected issues with comms being lost on a few devices at about the time the backups are taking place - by default 01:00 Hrs I think...

(CID:96043104)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2024-04-10 01:14 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2024-04-10 01:14 AM

We do have about 300 APC devices monitored with DCE and since we added the last 50 devices we are also getting frequent "communication lost" alert from random devices... we tried to increase poll rate, timeout delay and retries, but without any luck... i'd be interested in getting a solution for that.

(CID:124526893)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2023-10-31 11:21 PM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:22 AM . Last Modified: ‎2023-10-31 11:21 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of