Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2024-04-03 11:53 PM
Hello everyone,
please how do i pull logs from a backup file?
I only have access to 40-45 days logs on DCE and i also plan on adding more devices.
please advise
(CID:137102968)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2024-04-03 11:53 PM
Wow. So what would you advise i do?. 83.6% of the available 4GB storage space has already been used up and we still have some devices to add.
(CID:137103932)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2024-04-03 11:53 PM
Dear ADEKUNLE AGBOKE,
Please tell us about what logs you ask?
Are you interested in event logs for devices, that are monitored by the DCE-server? Or are you interested in logs of access and user actions in the DCE-clients and/or web-GUI? Or are you interested in the internal system logs of the DCE-server?
With respect.
(CID:137103085)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2024-04-03 11:53 PM
Hi,
I mean the internal system logs of the DCE-server. E.g. i want to be able to pull temperature, humidity, power data on the GUI of DCE but from a backup file
(CID:137103151)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2024-04-03 11:53 PM
Dear ADEKUNLE AGBOKE,
From your comments:
I mean the internal system logs of the DCE-server. E.g. i want to be able to pull temperature, humidity, power data on the GUI of DCE but from a backup file
Regarding terminology: the internal system logs of the DCE-server have nothing to do with devices, their sensors and alarms. Internal system logs of the DCE-server are the logs of the OS and DCE-server software and no more.
E.g. i want to be able to pull temperature, humidity, power data on the GUI of DCE but from a backup file
This is absolutely impossible, since what you want is not stored in any logs. Temperature, humidity, power data, etc. of the devices are written and stored exclusively in the embedded relational database of the DCE software.
Of course, this embedded relational database is saved in the full backup of the DCE-server. But this does not mean, that this database can read the DCE-client from the full backup of the DCE-server.
If you have more questions, please ask.
With respect.
relational
(CID:137103254)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2024-04-03 11:53 PM
Wow. So what would you advise i do?. 83.6% of the available 4GB storage space has already been used up and we still have some devices to add.
(CID:137103932)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2024-04-03 11:53 PM
Hi,
If your storage space is getting near it's maximum, add an extra drive to your DCE VM (no NOT increase the current drive size!!!). You can add another drive that can be as big as you want...say 100G or 1TB.
Steve
(CID:137103951)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:30 PM . Last Modified: 2023-10-22 02:54 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.