In one of our project, client wants to have integration with Siemens BMS and our DCIM.
Requirement is some devices like Vesda panel, fire alarm panel, power distribution boards etc. that are wired to BMS must also be seen in DCE and so we can map to DCO floor layout.
Siemens BMS is using Bacnet/IP protocol.
I heard about Automation Server from Schneider BMS that can do the protocol conversion for DCE to have sensor values from all devices using Bacnet/IP. Please anyone can provide more details of it?
(CID:110004804)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:51 AM . Last Modified: 2024-04-08 04:03 AM
Hi shemilusman
We've successfully used the Building Automation Server to act as a gateway to provide modbus/TCP info to DCE. Your best bet to progress this is work with your local SE Buildings BU team as you will need to have their engineering support to install and commission the BAS. Once the setup is finalised and you know what devices and modbus registers you need, you can have a DDF created.
Cheers
Ed
(CID:110004866)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:51 AM . Last Modified: 2024-04-08 04:03 AM
Hi shemilusman
We've successfully used the Building Automation Server to act as a gateway to provide modbus/TCP info to DCE. Your best bet to progress this is work with your local SE Buildings BU team as you will need to have their engineering support to install and commission the BAS. Once the setup is finalised and you know what devices and modbus registers you need, you can have a DDF created.
Cheers
Ed
(CID:110004866)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:51 AM . Last Modified: 2023-10-22 02:46 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.