IT Optimize tab CPU usage graphs are empty

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • IT Optimize tab CPU usage graphs are empty
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
8
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

IT Optimize tab CPU usage graphs are empty

Hello.

In the IT Optimize tab, whenever I try to check the CPU usage of any of the discovered servers of my datacenter, the associated cpu usage graph appears in blank.

 

 

 

 

I have checked ITO server and configuration is OK, but the Intel Data Center Manager component shows no measurements, I don't know if it is related to that problem.

 

Does anybody know what could be the issue?

Thanks.

(CID:93915129)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
0
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Hello Manuel.

I'm adding to the previous responses you have already received.

The Cisco UCS Manager tool is separate from IT Optimize. The polling in that case is performed directly from StruxureWare DC Operation to Cisco's UCS Manager.

If I look at the Intel DCM screenshot you attached I noticed the datacenter hierarchy pane (on the left side) is empty. This means no devices have been discovered using IPMI protocol using the server discovery wizard in IT Optimize.

Kresten's previous comments are correct in that to receive CPU utilization data you must discover the blades individually using one of the OS based protocols in IT Optimize. This includes WMI, SSH, and VMware protocols. The IPMI protocol does not currently return CPU utilization information, but it does return avg and peak power and server inlet temperature information assuming the server/blade's management card supports these objects.

Regards

Greg Sterling

(CID:93915189)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
2
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

Hi Manuel,

Since you show the DCM interface I expect the device is discovered using IPMI? I think the issue might be the device needs to be discovered with some OS level protocol.  In order to get CPU utilization you must also discover each individual device using an OS based protocol like WMI, SSH, or VMware.

 

 

(CID:93915147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

In response to DCIM_Support
0 Likes
0
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

Hello Søren.

I have used the external system configuration to add this device, it is a UCS 5108 blade server chassis with four blade servers B200 M3 within. I have not used ITO to launch a discovery over the single blade servers.

I thought that adding the Cisco UCS Manager as an external system would be enough to get the data.

 

So to get the data, Do I need to launch a discovery with ITO server using a specific protocol (apart from adding Cisco UCS Manager as an external system)?

 

Regards

(CID:93915218)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

In response to DCIM_Support
0 Likes
0
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

Hi Manuel, Currently the Cisco UCS manager integration is only done at a power information level. That means additional discovery of the blade(s) using OS based protocols in ITO is needed in order to get the CPU information provided as well.

(CID:93915242)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
0
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:34 AM . Last Modified: ‎2024-04-10 12:50 AM

When was the device discovered? Getting historical data is not instantly. It can only have historical data from the time it was discovered. With what protocols was the device discovered? It is not possible to get CPU data from a device that is only discovered through IPMI. The screenshot from Data Center Manager indicates that nothing was discovered through IPMI.

(CID:93915155)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
0
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Thanks Kresten, I will check the protocols used, but I added it as an external system (Cisco UCS Manager).

(CID:93915171)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

Hello Manuel.

I'm adding to the previous responses you have already received.

The Cisco UCS Manager tool is separate from IT Optimize. The polling in that case is performed directly from StruxureWare DC Operation to Cisco's UCS Manager.

If I look at the Intel DCM screenshot you attached I noticed the datacenter hierarchy pane (on the left side) is empty. This means no devices have been discovered using IPMI protocol using the server discovery wizard in IT Optimize.

Kresten's previous comments are correct in that to receive CPU utilization data you must discover the blades individually using one of the OS based protocols in IT Optimize. This includes WMI, SSH, and VMware protocols. The IPMI protocol does not currently return CPU utilization information, but it does return avg and peak power and server inlet temperature information assuming the server/blade's management card supports these objects.

Regards

Greg Sterling

(CID:93915189)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

0 Likes
0
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2024-04-10 12:50 AM

If I understand correctly: power level information can be gathered by using UCS Manager integration (without ITO modul).

In that case why I cannot see it? Integration has been done more than one week:

 

(CID:106892114)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2023-10-31 11:19 PM

0 Likes
0
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:35 AM . Last Modified: ‎2023-10-31 11:19 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of