I would like to create a graph of cooling system fan speed, is that possible?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • I would like to create a graph of cooling system fan speed, is that possible?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:17 PM . Last Modified: ‎2024-04-08 01:40 AM

0 Likes
12
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:17 PM . Last Modified: ‎2024-04-08 01:40 AM

I would like to create a graph of cooling system fan speed, is that possible?

I have several APC In-Row cooling systems in a group.  I would like to create a graph or table showing the fan speed of each unit in the group.  I can find sensors for the fan speed control (Automatic or Manual) and the Fan Speed Preference (Medium-Low in my case), but I cannot see a sensor for the current fan speed as a percentage.  Does this sensor exist and can be it be placed on my monitoring dashboard?

(CID:112624040)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

Hi Eric, does, the web UI of the In row display the fan speed?   From recollection I think they do - it's a pretty important sensor I think.

If it does, that's good news, if not, it probably means you're not going to see it in DCE (via the InRow's SNMP agent).  You can see what the InRow SNMP agent exposes by doing a sapnwalk

View the results, if the sensor is present, u can request a DDF update (may be worth doing this straight away?). If there's no fan speed present, you may need an InRow firmware update.  Check with your cooling support people.

Or perhaps the inRow exposes the sensor via modbus?

If you're lazy (like me), try the DDF update 1st.

Cheers

Ed

(CID:112624096)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

0 Likes
9
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

Hi Eric,

I'm currently looking at an Inrow RC unit and it has a sensor for Unit Fan Speed in percentage.  I'm not sure for other Inrow units if they have this type of sensor available. 

 

If anyone else has information about this sensor on other units, feel free to jump in.

 

Kind regards,

John

 

(CID:112624177)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

Eric,

Just to add to this, You can find the sensor by going to reports, Choosing "Other Numeric" for the report type. I then searched for InRow when choosing devices and device groups and for selecting sensors, I simply searched with the word speed.

 

Steve

(CID:112624359)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

I have APC InRow Full-Rack units (IR25) and I do not see fan speed as one of the sensors.  It does show in the Web UI for the cooling units.  

(CID:112626306)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

Hi Eric,

 

Please make sure you're up to date on the unit's firmware. You can check here for newer DDF files or if you have the newer DCE versions, you should already have the newer DDFs.

I spoke to the air guys and they said the inrow 25 is an RP unit. I have one here and it lists fan speed. I'm running DCE 7.4.1 and the Network Air RP25 is version 17. IN case that's not the right DDF, the IR Gen 3 is version 2 and the IR Gen 2 is version 7

 

Steve

(CID:112626310)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

I am running DCE version 7.4.1.5.  When I choose to Apply Updates in DCE, none of the cooling units show up as needing an update; I assume that means they are up-to-date on firmware?  

I just started using DCE, so hopefully this will get easier, but I don't know what you mean about Generations and versions of DDFs.  

(CID:112626739)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

Hi Eric,

 

DCE purposefully does not update firmware on air units. Air units, depending on their firmware, can turn off during the firmware upgrade process. We don't want to upgrade all units in the facility and potentially turn them all off. You wouldn't be too happy with that. 

Do you have DDF files similar to what I had previously shown? I would expect that the options would be there in 7.4.1 but I don't have exact DDF version numbers by DCE version.

If you launch to a device and go to help and about, you can get the firmware revision.


Steve

(CID:112626817)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

I found the Cooling unit firmware under Unit -> Identification:

Controller firmware 6.8.0
Hardware revision C8
VFD Software version 01.08

I have not added any DDF files, we simply installed the OVA (VMware appliance) and performed a discovery.  The cooling units, PDUs, and UPSs were detected but I can't find a sensor for fan speed.  I did create a request for an updated DDF yesterday in case that will help, although it sounds like those sensors should already be there?

 

(CID:113182465)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:18 PM . Last Modified: ‎2024-04-08 01:40 AM

Hi Eric,

 

It's the NMC firmware that you'd be concerned with as that is what is responsible for both the web and the SNMP information that DCE pulls. Here's an example of the older network management card's firmware which has the value:

...and here is another unit with the newer NMC and firmware (this one is a UPS though) from about->network:

 

 

 

(CID:113182476)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:19 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:19 PM . Last Modified: ‎2024-04-08 01:40 AM

I think I found it under Administration -> General -> About:

Application Module & APC OS are v3.7.5

 

 

(CID:113182491)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:19 PM . Last Modified: ‎2024-04-08 01:40 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:19 PM . Last Modified: ‎2024-04-08 01:40 AM

So there are higher versions and I don't have firmware that old to test but I would expect to see that sensor. If you have an SNMP utility, maybe you could poll this OID for fan speed:

.1.3.6.1.4.1.318.1.1.13.3.3.1.2.2.12.0

Or this one:

.1.3.6.1.4.1.318.1.1.13.3.3.2.2.2.12.0

These are for 2 different RP units.

If there is no SNMP variable for it, tha's one reason DCE wouldn't see it

(CID:113182493)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:19 PM . Last Modified: ‎2023-10-22 02:39 AM

0 Likes
0
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:19 PM . Last Modified: ‎2023-10-22 02:39 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore