EcoStruxure IT forum
A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:50 PM
This question was originally posted on DCIM Support by laurent dulac on 2019-06-05
Hello,
I am using MIB Browser and have loaded the PowerNet MIB. I managed to get some parameters of the MIB (under the apcmgmt folder), however it does not work for SNMP objects under the products folder (object not found).
I would like to be able to read with SNMP "gets" the status of my sensors (temperature, humidity, doors status open/closed). Could you please help me to do so ?
Thanks
(CID:144314080)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:50 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-06-05
Hi Laurent,
Before looking for the correct OID, we'd need to know what product you're using and what sensors.
Thanks,
Steve
(CID:144314139)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:50 PM
This comment was originally posted on DCIM Support by laurent dulac on 2019-06-06
Hello Steve
I have the Netbotz 250 (model NBRK0250, HW Rev 05, FW Rev 0.7.6).
The wired sensors are
- door switch : NBES0302
- Temperature and humidity : AP9335TH APC.
Regards
Laurent
(CID:144868354)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:50 PM
This comment was originally posted on DCIM Support by laurent dulac on 2019-06-06
Hello,
By chance I have been able to find the information into the MIB.
The doors sensors status can be fetched in the table : memDoorsSensorsStatusTable.
The temperature / humidity sensor status can be read under : memSensorsStatusTable.
Both are tables so a snmptable command must be used.
Regards
(CID:144868352)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:51 PM
This comment was originally posted on DCIM Support by laurent dulac on 2019-06-06
Thank you for the support
(CID:144868356)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 07:51 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.