Dear Expetrs,
The customer has 1 symmetra UPS 500 acts as UPS B and Two symmetra UPS 250 act as UPS A how to configure the two UPSs 250 to act as UPS A in DCO 8.1?
BR,
Sameeh
(CID:126172996)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:42 AM . Last Modified: 2024-04-05 04:03 AM
Hi Sameeh ahmad, thanks for posting. Let's hope you find your answer here.
Kind regards
Ditte
(CID:126173358)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:42 AM . Last Modified: 2024-04-05 04:03 AM
Hi Sameeth,
Not sure I understand what it means exactly by two UPSs to act as one, serial addition of two units or parallel? I don't think that's directly supported in DCO. I think in either case a possible work around might be to create a single UPS.
Kind regards
(CID:126173455)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:42 AM . Last Modified: 2024-04-05 04:03 AM
Hi Jeff,
There are two UPSs 250KW working in paralle. and these two 250KW UPSs are working in parallel with 500KW UPS.
If I replaced the two UPSs 250 KW by a single UPS 500KW I will not be able to associate the UPSs correctly, what do you recommend ?
BR,
Sameeh
(CID:126173536)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:42 AM . Last Modified: 2024-04-05 04:03 AM
As Jef Faridi suggested, if the UPS are configured in parallel, you should model them as one UPS in DCO (with the combined capacity of the two UPSs - 500KW).
In order to get the associations from DCE to work, I would create a UPS object with zero capacity and a small form factor, and then place that next to the big UPS in DCO. That way, you get a UPS object where you can associate DCE alarms.
Hope this helps.
/Christian
(CID:126173742)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:42 AM . Last Modified: 2024-04-05 04:03 AM
Thanks Christian for your reply, I'll follow your recommendation.
BR,
Sameeh
(CID:126173763)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 01:42 AM . Last Modified: 2023-10-22 02:28 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of