Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

How to add DCO CPU resources?

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How to add DCO CPU resources?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
76
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:36 PM

0 Likes
6
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:36 PM

How to add DCO CPU resources?

This question was originally posted on DCIM Support by Yonker Wang on 2017-08-03


DCO Slow response . Restart DCO one time, it costs about 4 hours.

If Two users log in at the same time, One of them cannot load the Client view.

Check the system, The CPU is used 210% always in DCO , below.

How to add DCO CPU resources?

(CID:123343894)

Labels
  • Labels:
  • Data Center Operation
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:36 PM

0 Likes
4
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:36 PM

This answer was originally posted on DCIM Support by spezialist on 2017-08-03


Hi Yonker Wang,

Most likely you have DCO-server working as a VMware VM appliance. Therefore, firstly, it is necessary to check whether the hardware resources allocated to your DCO VM correspond to the minimum requirements that can be found on the page Recommended StruxureWare Data Center Operation server configuration:

Server requirement guidelines (minimum)
  • CPU: 4 cores minimum. We recommend 8 cores
  • Memory: 16 GB RAM (absolute minimum requirement)
  • 100 GB storage, speed minimum 170 MB/s
  • Cluster network: 1 Gbps connection between nodes
  • Disaster recovery network: 10 Mbps with low latency <100 ms 

If your'e installing DCO on an existing server, note that DCO claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). Therefore, you may experience issues if you have other applications running on the server, such as surveillance and monitoring agents.

If this is not the case, you should contact your VMware administrators to allocate the missing hardware resources for the DCO VM.

With respect.

(CID:123343908)

See Answer In Context

Reply
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:36 PM

0 Likes
4
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:36 PM

This answer was originally posted on DCIM Support by spezialist on 2017-08-03


Hi Yonker Wang,

Most likely you have DCO-server working as a VMware VM appliance. Therefore, firstly, it is necessary to check whether the hardware resources allocated to your DCO VM correspond to the minimum requirements that can be found on the page Recommended StruxureWare Data Center Operation server configuration:

Server requirement guidelines (minimum)
  • CPU: 4 cores minimum. We recommend 8 cores
  • Memory: 16 GB RAM (absolute minimum requirement)
  • 100 GB storage, speed minimum 170 MB/s
  • Cluster network: 1 Gbps connection between nodes
  • Disaster recovery network: 10 Mbps with low latency <100 ms 

If your'e installing DCO on an existing server, note that DCO claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). Therefore, you may experience issues if you have other applications running on the server, such as surveillance and monitoring agents.

If this is not the case, you should contact your VMware administrators to allocate the missing hardware resources for the DCO VM.

With respect.

(CID:123343908)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:36 PM

In response to DCIM_Support
0 Likes
0
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:36 PM

This comment was originally posted on DCIM Support by Yonker Wang on 2017-08-04


 

Thanks for your help~!

 

(CID:123344284)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:37 PM

In response to DCIM_Support
0 Likes
0
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:37 PM

This comment was originally posted on DCIM Support by spezialist on 2017-08-04


Hi Yonker Wang,

Thanks for the feedback: it will be very useful if you let us know whether the problem is solved or not.

With respect.

(CID:123344286)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:37 PM

In response to DCIM_Support
0 Likes
0
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:37 PM

This comment was originally posted on DCIM Support by Yonker Wang on 2017-08-07


Hi team,

We reinstalled the DCO, give the DCO more Resources, according to Server requirement guidelines (minimum) , have solved the problem.

(CID:123344738)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:37 PM

In response to DCIM_Support
0 Likes
0
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:37 PM

This comment was originally posted on DCIM Support by spezialist on 2017-08-07


Hi Yonker Wang,

Thank you for your feedback.

With respect.

(CID:123344792)

Reply
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:37 PM

0 Likes
0
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2020-07-03 06:37 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc